Guest viewing is limited
View the thread, titled "TT or PME" which is posted in Domestic Electrician Forum on Electricians Forums.
Just been to look at a job and found this. It's an overhead supply so could be pme at the post but no earth back to the cutout and (although admittedly i didn't have much time to have a proper look) I didn't spot a rod.
I'm thinking advise the customer to get the dno to come and have a look and fit an isolator while they're at it.
Any thoughts?
Thanks!
Is "main supply earth" an assumption or confirmed? could it not be another bond?
Low reading could be a parallel path of connected metalwork, eg earthing of boiler/gas pipe (by both bonding and/or cpc's) going to a neighbour's TNC-S connection? Did you do a proper Ze ie disconnecting the "main supply earth" to test it?
If unsure about a TNC-S connection, a low resistance check N-E is a first thought...
Update from customer: National grid have been round, removed the PME sticker and informed the customer they'll need an an earth rod installing.
One small sticker causing so many problems!
I know we can't guess but, if I had to guess, I bet there's an earth rod somewhere, probably beneath a new porch or conservatory!
If you really want to @aliensbrains you could let us know what Ra you get on your new rod, as we like things like that :D
Interestingly, national grid also recorded 0.27ohm L-N, the exact same reading I got when I measured Ze from the 10mm 'main earth' in the consumer unit.
So now I'm thinking, what is the best thing to do with that 'main earth' once I've installed a rod...
I'm guessing the quotation marks for 'main earth' are because you know you can't assume it is the main earth without seeing what it is attached to. I can't see a reason to disconnect it once the rod is in place, but may stand corrected.
Correct. Neither I or the DNO can confirm where this is connected but given the readings it seems sensible to assume it's an unofficial PME connection.
Therefore as you say, my current thinking is to leave it in place, and make a note on the certificate referencing the DNO job number, to explain the situation (and the low Zs values) for a TT system.
Leave the rod in place as recommended in bs7671
Surely an "unofficial" TNCS connection still has to go to the incoming supplies neutral/PENl conductor, not "disappear off somewhere?"
Also, it it were an "unofficial" TNCS connection where PME isn't present (tip; it can't by definition be an unofficial PME, PME and TNCS do not mean the same thing) then connecting it to the houses earth might not be the best idea
Agreed. If both me and the DNO recorded 0.27ohms then it appears this cable must be connected to the neutral somewhere. But the DNO have still asked for a rod.
Can you explain why connecting this back to the earth in the CU is not the best idea? What would you suggest is a better approach?
Agreed. If both me and the DNO recorded 0.27ohms then this cable must be connected to the neutral somewhere. But the DNO have still asked for a rod.
It's all to do with the danger of losing the PEN conductor which would make the entire earthed parts of installation live; PME is the mechanism by which TNC-S is considered safe, ostensibly connecting to multiple extra earth rods along the conductors route (hence multiple earthing) but theres also other requirements such as crimped rather than screwed line tap connections. If the DNO have removed the PME label from the service head it suggests the supply side doesn't meet these requirements.
I get what you are saying...
I'm guessing the earth rod would be too high resistance to prevent the issues in the event of a broken PEN?
Therefore it would seem sensible to disconnect this cable from the CU and safely terminate? But this presents new issues with having a green and yellow cable that I suspect is tied to the incoming Neutral hanging in the wall.
Reply to the thread, titled "TT or PME" which is posted in Domestic Electrician Forum on Electricians Forums.