Just been to look at a job and found this. It's an overhead supply so could be pme at the post but no earth back to the cutout and (although admittedly i didn't have much time to have a proper look) I didn't spot a rod.

I'm thinking advise the customer to get the dno to come and have a look and fit an isolator while they're at it.

Any thoughts?

Thanks!

PXL_20241219_173333858.jpg
 
Is "main supply earth" an assumption or confirmed? could it not be another bond?

Low reading could be a parallel path of connected metalwork, eg earthing of boiler/gas pipe (by both bonding and/or cpc's) going to a neighbour's TNC-S connection? Did you do a proper Ze ie disconnecting the "main supply earth" to test it?

If unsure about a TNC-S connection, a low resistance check N-E is a first thought...
 