Don't get the PSCC & PEFC mixed up.
The PEFC is what you are after so you do not multiply by x 2 or 1.73 as it is a single phase calculation between a phase and earth.
230/03 = 766A
So your PEFC is 766 Amps
I hope this makes sense.
cheers pal makes a lot of sense, as i said earlier your pssc would always be higher so in my eyes its a silly question anyway
exam in two days! sheeting myself
bit of a silly one this
state two reasons for the prescribed sequence of tests prior to energising a new circuit
The sequence of tests is designed so that:
1 Safety is foremost-all dead tests are first and continuity of CPC is confirmed.
2 The results/faults identified in the previous test can influence the next so the sequence is designed to minimise this.
is there any reference to this in the books?
another one - state what the designer may take into account when determining maximum demand?
is this the type and use of the installation
Diversity
a bs 1361 fuse is to be used to provide overcurrent and fault protection for a new circuit. State the effect on the operation of the fuse when the following conditions occur if the fuse was installed in the neutral conductor
a. overload fault
b. earth fault
c. short circuit fault
a. fuse would blow
b. no effect
c. fuse would blow
have i got this right, i know this has already been discussed somewhere but wanted to try it off the top of my head
sorry to be a pain in the butt
during the course of the inspection one of the single phase radial circuits supplying an item of fixed electrical equipment is to be checked for voltage drop compliance. The circuit has the following characteristics
load current = 45 amp
circuit length = 80 metres
live conductors = 10mm
a. using the information given in figure 1 determine whether the circuit meets the requirements for voltage drop. Show all calculations
80 x 1.83 x 2 x 1.2/1000 = 0.35136
v = ixr
vd = 45 x 0.35136 = 15.8 volts
230v circuit 5% = 11.5 volts
so circuit does not comply
is this correct?
Your answer is right it does not comply.
I would have used the equation (mV/A/m)x Ib xL /1000 4.4 X 45 X 80 /1000 = 15.84 V
I see you have used (m ohms/m) x 2 x1.2 which gives you the the mV/A/m anyway.
On the question paper it will give you a table of mV/A/m for the different sizes of cables they won't expect you to remember them its the equation that you need to remember.
Good luck with the exam!!!
v = ixr
is this correct?
Yep
:party:
dont get too excited the next part of the question got me puzzled
State
i. a suitable observation to be recorded on the periodic report if the voltage drop fails to comply
ii. one action which could be taken to rectify the situation in i. above
i. circuit blah blah failed volt drop test code 2
ii. reduce length of circuit?
hi there
The simple answer is you are not speaking the city and guilds lingo mate and thats just it!
I have a C course qualification and i failed it first time !! 2391 that is
The simple fact then was you have a bank of questions which require a standard answer and if it aint standard you are not either !!
We just learnt parrot fashion questions and the way to answer them and at a speed which you need to get all the crap they want down
in the right time and manner.
i dont doubt you are a very good sparkie mate i would like to think i am as well as i have now got 2391 the old 2400 design and verification
qualifcation and that took its toll as well i can tell you.
get as many past paers and sit down and look for a repeat pattern over the years things may have changed new bits of regs but there are only certain areas of testing they can look at mate
the format used to 10 or 20 question short one hour and some lopnger one about two hour six i think
other on here will put me right about that so practice in short sessions to get your speed up and if at the end opf the exam you have not filled 20 or so pages you have a good chance finish early you almost certainly failed unless your a speed writer and einstein
good luck and all the best
An Awful Feeling This
gap30,
trev,
TrueNAS JBOD Storage Server