There are always going to be situations such as you have described due to horrendous soil/ground conditions, and you're solution of an upfront S type, backing up any standard 30mA RCD's is the route i would also take, in such circumstances...

I too have a good amount of chalky soil on my property in Cyprus, but thankfully not to the extent of causing me major problems on my own system...
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?
Regards
 
Interesting how you give special thanks to the two very people that most on here would regard as being at complete opposite ends of the spectrum with regards to their opinions on domestic TT systems yet refer to others opinions as drivel?
I was thinking the same, funny world
 
No petty arguments on the thread ?????

Most of us on here respect E54 highly, he is entitled to his opinion as much as other highly respected posters are, we were pulling his leg somewhat as we already know what his opinion is lol

That doesn't mean we cannot have our own opinions either, and if you notice we did not say he was wrong, just we all follow the regs which are sometimes badly written and open to interpretation, or sloppily written which implies one thing but could equally mean something else entirely.

Discussions are a good thing, no ?

If you actually understood TT systems a) you would not have posted in the first place, and b) you would see both sides of the debate which was going on in the background, but sadly this appears to have been lost on you.
 
Last edited:
Was trying to refrain from posting again on this thread, but that last post by sparky68 was just beautiful!
 
What was it you said:

"I got a bite! A big one! C'mon lads, get the landing net out ready, this one's gonna be a wriggler!"

Sorry that I'm not interested in winning popularity contests and taking sides in petty arguements.

Neither am I?

I thanked everyone on the thread especially those 'wirepuller' & 'Engineer 54' whose advice I followed and which resolved my situation and in fact got me extra work.

Huh? That's like saying you support Tottenham and Chelsea at the same time? Is it even possible???

However if this leaves you feeling a little under appreciated:

I'm not after your appreciation, nor you patronisation, just the loosening up of your humour belt. We're not here to hate on each other, we're here to offer each other advice and at the same time have a laugh without the fear of having our professional opinions being denounced as drivel. Chill out man!
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

Indeed as my original post clarified "TT virgin" my knowledge on TT is limited and has now been enlightened somewhat.

The end result is I learned and won extra business. Both of which I am thankful for.

It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.
 
Sorry to be thick, but how does an upstream s,type provide more protection, unless you nail the tails ?
Regards

It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.
 
Sorry if I've upset the apple cart gents.

I just find it strange that my singling out of the two individuals whose advice I followed was questioned.




It appears that I have affronted one of the inner circle and the wagons are circling so before this gets silly.

Once again thanks for the lessons and the input.

Best regards to you all.

Not at all, it was referring to other valued posters/posts as "Drivel" which comes across badly
 
I just find it strange that my singling out of the two individuals whose advice I followed was questioned.

It wasn't your singling out of Eng and WP I was questioning, it was the ommission of regognition for the other contributors to the thread and instead, referring to their opinions/advice as drivel .
 
It will provide backup in the unlikely...(although some would argue likely)...event of the 30ma RCD failing to trip on an earth fault.After all on a 'normal' uk TT system with an Ra exceeding that which will operate an OCPD you are completely reliant on a single RCD for earth fault protection.

And it is required when a metal CU/DB is used, it is TD (time delayed) to provide some discrimination to the final circuits 30mA devices so that it doesn't knock the whole lot off in the event of a fault
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Max Ze for TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
137

Advert

Thread statistics

Created
MBEINST,
Last reply from
Guest 004,
Replies
137
Views
58,401

Advert

Back
Top