16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb | Page 2 | on ElectriciansForums
Discuss 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net
Manchester
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.
Cheers
if the charger is designed to plug into a 16A socket, then the 16A socket is sufficient.
going by the argument of whoever coded it, that means we need to fit 13A socket circuits with a 13A MCB.
20 amp should be fine supplying your 16amp socket as you say its covered in OSG part H3.
Out of interest have you hit mainly drains installing your earth rods for your EV chargers ?
I don't know! Scary every time though. Bought a cat scanner for cables but still!! 18th edition takes out the "where reasonably practical" bit. So expect a lot of People hitting utilities
16 amp commando and the osg.
[ElectriciansForums.net] 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb
Because it's an ev charger and like I said in the original post charges for 16 amps constant. Over time I have had them wear the bi metallic strip and start to trip. 20 amps takes the stress off and complies with IET on site guide.
This suggests it is either a poor choice of MCB or actually pulling more than 16A.
A single 16A socket shouldn't need to have an ocpd of more than 16A supplying it, if it does then it is most likely overloaded.
Reply to 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net