View the thread, titled "16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb" which is posted in UK Electrical Forum on Electricians Forums.
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.
Cheers
It would seam he has fallen into the trap of Ib<In<Iz which is really only applicable if overload is a factor.
As this is a fixed load then he can't code it based on this alone.
but Iz is the current capacity of the cable, not related to the socket.
Exactly and when I question what reg they are coding it under I've heard nothing?
regulation 000.00.000. thou shalt not code anything that does not contravene any of the other regulations that we, the all knowing, all seeing, IET, want to dream up to make electricians lives more difficult than we have already made them. ..........
......... excuse the break. amendments to the 18th neeed to be drafted.
these will, of course incur charges at you normal rates.
It's a bit of a stretch to call a socket outlet a fixed load isn't it?
And the fact that when connected via a 16A mcb it trips on overload it suggests that the 16A socket is overloaded.
Reply to the thread, titled "16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb" which is posted in UK Electrical Forum on Electricians Forums.