Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.
Cheers
I've lost track dave, I thought this thread was about coding something incorrectly, then it's went to overloaded 16 amp socket.
It started out that way, but then the OP revealed that the reason he fitted a 20A ocpd was that the load causes a 16A ocpd to trip on overload.
You have had your work queried during a subsequent inspection.
You know that the situation is not contravening the wiring regulations and the inspector cannot provide a regulation to match the C2 coding.
Advise the customer of this and finish the discussion.
Unless anything further comes up there is nothing to pursue.
You can consider the merits of the comparison of the protective device and the rating of an accessory but that is not really an issue in this case despite what you have mentioned about the loading and MCB operation. So long as the socket is not taking more than 16A then there is no problem.