View the thread, titled "16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb" which is posted in UK Electrical Forum on Electricians Forums.
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.
Cheers
I wouldn't Code it at all but if a 16A device trips then it is inadequate for the connected load and this must also apply to the 16A socket, change it to a 32A socket.
if the charger is designed to plug into a 16A socket, then the 16A socket is sufficient.
going by the argument of whoever coded it, that means we need to fit 13A socket circuits with a 13A MCB.
16 amp commando and the osg.
Because it's an ev charger and like I said in the original post charges for 16 amps constant. Over time I have had them wear the bi metallic strip and start to trip. 20 amps takes the stress off and complies with IET on site guide.
This suggests it is either a poor choice of MCB or actually pulling more than 16A.
A single 16A socket shouldn't need to have an ocpd of more than 16A supplying it, if it does then it is most likely overloaded.
Reply to the thread, titled "16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb" which is posted in UK Electrical Forum on Electricians Forums.