You could put a Henley block in and split the tails like you suggested, but there should be 1 point of isolation for the whole installation,
Really ............ reg number please?
Discuss Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
You could put a Henley block in and split the tails like you suggested, but there should be 1 point of isolation for the whole installation,
Isolator? you will need an OCPD for the circuit, why 16mm2? did you calculate the load required? I bet that is overkill, also why a joint in a new cable run? have you got test equipment? there are plenty of other answers needed to the questions already asked to be fair.
Really ............ reg number please?
Nah... I was going to suggest a 10a light switch!! LolWhy an isolator? It needs an OCPD not just a switch.
Bbb p121What book is that in mossep?
Thanks, wasn’t taking the pi$$ I’m still on the byb and couldn’t find it...Bbb p121
Its in the BYB too, not sure what page though but probably a similar reg number.
Thanks spoon I’ll be in there later.537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Thanks mossepIts in the BYB too, not sure what page though but probably a similar reg number.
Its OK.. I still haven't booked my 18th exam. Don't think I'm gonna get a place before Jan either .Thanks, wasn’t taking the pi$$ I’m still on the byb and couldn’t find it...
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.
If not hundreds of thousands of properties could be deemed dangerous
Youve changed your tune haha
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.
A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.
BYB page 154
Can you believe they've deleted 537.1.6 from BBB. I think we will have the same label at 514.15.1 and perhaps 537.2.7 (new) which says isolators to be clearly identified.In such a case where there are 2 boards or more, you could argue that 537.1.6 would then apply ................... (BYB p 154)