Isolator? you will need an OCPD for the circuit, why 16mm2? did you calculate the load required? I bet that is overkill, also why a joint in a new cable run? have you got test equipment? there are plenty of other answers needed to the questions already asked to be fair.

I would imagine the joint is because it easy to terminate an SWA in an external adaptable box, and then run T+E internally to the fuse board. Not that uncommon really, aesthetically it might even look better on the outside wall as you'll struggle to put a neat bend in a 16mm SWA as it goes through the wall. Assuming its been done right what problems do you see with having a joint?
 
Its in the BYB too, not sure what page though but probably a similar reg number.


537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154
 
Nothing wrong with a Joint if it is done right, and if there is no other way, I don't think the job has been planned properly at all, a 16mm2 armoured and 16mm2 t&e for a very small out building with one ring a heating mat and a couple of lights, plus direct connection to an isolator and no OCPD is of concern, I appreciate the OP is very inexperienced and such should answer questions aimed at him by the other guys on here, I have seen him post since these questions and not answer. Has he concidered RCD protection for example, what type of earthing arrangement, is it notifable work? a lot to take in for a very basic job, hopefully he will start again and let us all into his thoughts so we can try to help properly. By the way that Bob the Builder book isn't great, I have the set, that story is one of the worse ones :D
 
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154
Thanks spoon I’ll be in there later.
 
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154

Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.

If not hundreds of thousands of properties could be deemed dangerous
 
Which is open to interpretation ... A main switch per fuseboard and per switch fuse could serve to provide the necessary isolation.

If not hundreds of thousands of properties could be deemed dangerous

I don't think it would mean properties would be dangerous, just poorly designed.

Would you have the same opinion if you went into the mains room of a large factory and had to shut off the power in an emergency, and instead of having a single main isolation switch, you had a series of 15 randomly placed switch fuses and fuse boards? BS 7671 applies to all setups after all.
 
Not quite the same thing though is it. Two consumer units next to each other do not really create an isolation problem. Certainly not one which means it is essential to install a separate isolator next to them anyway.
 
MDJ - thanks for your reply. To clarify intent. Split incoming mains and install a CU house side that will feed 16mm to outbuilding. CU in outbuildings supplying one RFC one lighting circuit and 15m2 of UFH and two electric Velux. The reason for T&E into SWA was picked up in a post - for aesthetics as conduit into box outside looks better than trying to get 16mm SWA out and down a wall. Does this answer Qs or have i missed something? Thanks so far all. I was going to install a mains isolated while i was there as currently not one
 
I picked an example at the other end of the spectrum on purpose to be honest. The regulation doesn't say how many fuse board there needs to be before you need an isolator to turn it all off, it just says that every installation needs one at the origin.
 
537.1.4 A main linked switch or linked circuit-breaker shall be provided as near as practicable to the origin of every installation as a means of switching the supply on load and as a means of isolation.

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt both live conductors of a single-phase supply.

BYB page 154

In such a case where there are 2 boards or more, you could argue that 537.1.6 would then apply ................... (BYB p 154)
 
In such a case where there are 2 boards or more, you could argue that 537.1.6 would then apply ................... (BYB p 154)
Can you believe they've deleted 537.1.6 from BBB. I think we will have the same label at 514.15.1 and perhaps 537.2.7 (new) which says isolators to be clearly identified.
 

Reply to Sub main advice please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
642
Sounds more positive.
Replies
8
Views
479
  • Question
Not sure if I’ve understood this properly, but it appears to have parallels with my own installation. I highly dislike the idea of feeding SP...
2
Replies
49
Views
5K
You would treat it as a TT installation.
2
Replies
29
Views
1K
It's not really as simple as "you can do it" or "no you can't". PV downstream from any upstream shared RCD is a no-no. PV on a shared final...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks