I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.
 
I worked for years in electrical wholesalers and understand matters fine.
I reckon I do have a fault, however I cannot understand where. I tripped the in-house mcb and then disconnected the RCD, now when switched up it stays up.
Surely this means the fault is between the cu and the RCD, as I have thought until now, it’s simply a single length of cable within plastic conduit, even through the wall and right into the RCD! Thanks.
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
I had a customer did what the op tried to do ,he came of worse in the end .
 
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.

There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
Sorry misunderstood your description, my error
 
Can you post a photo of the RCD/board please?

Attached.

[ElectriciansForums.net] RCD refuses to switch on (up)
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
What you describe as an ELCB what make and type is it
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
As per my previous post; have you tried that?
yes, I replied above. The RCD stays on. I then reconnected the brown wire and it stayed on. As soon as I tried to connect the neutral the RCD tripped.
 

Reply to RCD refuses to switch on (up) in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
598
davesparks
D
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
730

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top