I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.
 
I worked for years in electrical wholesalers and understand matters fine.
I reckon I do have a fault, however I cannot understand where. I tripped the in-house mcb and then disconnected the RCD, now when switched up it stays up.
Surely this means the fault is between the cu and the RCD, as I have thought until now, it’s simply a single length of cable within plastic conduit, even through the wall and right into the RCD! Thanks.
 
I’ve run a 2.5mm t&e cable from a 16a cu in the house to the shed all in 20mm plastic conduit - say 7m. The shed has a BG garage unit with RCD and two ways, 5 and 16a.
In the shed is a final ring circuit with a spur for a fan and a LED style fluorescent fitting. The RCD refuses to switch on. Even with both ways switched off the RCD will not switch on.
I have checked all connections and can find nothing. I checked the mcb, previously used for an immersion heater, by connecting the lights wire into it and everything was okay.
Wired brown into mcb, blue to neutral bar and earth to earth bar all on the non-elcb side of a MEM cu. Other end as per instructions into RCD.
Any ideas please? I simply wanted this up and working before bringing a sparky in to test and certify.
I had a customer did what the op tried to do ,he came of worse in the end .
 
A Sparky should have been present / involved at all stages of the installation, for him to issue an EIC. Having two RCDs in series or on the same leg is a no no as well.

There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
Sorry misunderstood your description, my error
 
Can you post a photo of the RCD/board please?

Attached.

[ElectriciansForums.net] RCD refuses to switch on (up)
 
There are not two RCDs involved. As per the post the shed is being wired to the non-elcb side of the cu. The elcb in the cu protects only the two mcbs for the sockets. Other than the elcb there are only mcbs in the cu.
What you describe as an ELCB what make and type is it
 
Firstly I hope you know what you are doing and can carry out safe isolation?

Sounds like you may have a fault. You might have to get that sparky in earlier than you thought. What happens when you disconnect wiring from the load side of the RCD?
As per my previous post; have you tried that?
yes, I replied above. The RCD stays on. I then reconnected the brown wire and it stayed on. As soon as I tried to connect the neutral the RCD tripped.
 

Reply to RCD refuses to switch on (up) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
541
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
918

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
465
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
879
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top