It is yesThe programmer you have, is it a Honeywell ST9400c ?
I did ask to see your controls in another post as I suspected that you had that programmer.
Turn off the demand for hot water and heating.
Turn the cylinder and room stats up to ensure they both call for heat. (make sure you turn the cylinder down again when you have tested the programmer)
Using the override buttons you should see the green lights and hear two distinct clicks. The sound of the clicks are the important bits, so listen for them both.
If you only hear one click then the programmer is at fault.
What is the make and model of the ASHP please?
Speed reading this thread did I pick up correctly:
1a. you have a hot water tank and separate buffer hot water tank?
1b. The buffer tank contains the heated water for the radiator circuit?
2. as far as you know the installation control is S plan or some derivative of it?
3. you have a room thermostat(s), a hot water tank thermostat and a buffer tank thermostat?
4. One pump.
Did the system ever work correctly?
What solenoid valves do you have and their type - just post a picture of the label on them or the part number and make.
Please draw a sketch of the valves, pump, ASHP, tanks, rads water circuit.
Re your #53 - is there a link between terminals 11 and 12? I cannot tell from the image.
Such a link seems to be required for simultaneous space and water heating according to the manual.
That's correct there is a stat on the buffer tank, all pumps and MVs work when heat is called for just not the heat pump.No don't do any measurements.
So the fault is that the ASHP will never run up in demand to a space thermostat to warm the water in the buffer tank?
Please confirm whether there is a 'stat on the buffer tank - I'd expect to see one.
The programmer does have HW and CH selected to on and either in a timed on period or sert to constant?
Thank you, please see added pic to above post of stat on HPI have enough now to be getting on with. I hope to reply tomorrow morning.