Hi All

I’m presuming a standard pendant is a class 2 fitting as the earth terminals are not needed as it’s a plastic fitting and it only has an insulated 2 core going to the actual ‘lamp part’.

Am I correct in thinking this?

The reason I ask is Screwfix have replied to someone’s question that it is a class 1 and requires an earth? Even though it is only used to loop in/out.

Can anyone clarify this for me.

Thanks [ElectriciansForums.net] Is a standard Pendant a Class 2 fitting?[ElectriciansForums.net] Is a standard Pendant a Class 2 fitting?
 
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.
 
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.

Agree. But it's not classified as class II.
 
For flip's sake, that's my post blown out of the water. Cheers!

But then, hold on - that's only the holder part. The assembly is not class 2.
just checked a BG pendant and it has no symbols or markings to help us.
and for the first time ever, i have actually read the enclosed instruction leaflet and it also has no useful information.
 
just checked a BG pendant and it has no symbols or markings to help us.

I'm sure any assembly that has an earth point or an earth cable entering it cannot be classified as a class 2 device. I would put a fiver on it. And I'm from Yorkshire.

And if that has no symbols on it then that confirms it isn't class 2.
 
From definitions:

Class II equipment. Equipment in which protection against electric shock does not rely on basic insulation only, but in which additional safety precautions such as supplementary insulation are provided, there being no provision for the connection of exposed metalwork of the equipment to a protective conductor, and no reliance upon precautions to be taken in the fixed wiring of the installation (see BS EN 6 1140).
 
I believe pendants, or more specifically the lamp holder is a special case when it comes to regs.
Access to live parts, where anyone can easily stick a finger in and touch the pins.
Although I think new lamp holders don’t power up unless a lamp is fitted.

As for class I or II… A pendant is made up of a ceiling rose, basically a junction box, a length of 2 core flex and a lamp holder.
The double insulated symbol must only be for the lamp holder part.
 
There is no way that pendant holder it Class II is has exposed live pins. The part no is K1170RPWHI and the only site which shows that symbol is Amazon none of the other sites do.
So Amazon is adding unauthorised 'Double insulated' labels to a product?
Sounds a bit like my dubious market trader relative and his roll of self adhesive 'CE' labels.
 
So Amazon is adding unauthorised 'Double insulated' labels to a product?
Sounds a bit like my dubious market trader relative and his roll of self adhesive 'CE' labels.
Who knows but it is odd this product on other sites does not show it and its position and everything about it is odd.
 
My GF mum house has no earth on the lighting circuits, pre 1966 build, has some metal light fittings, she is 90 years old and does not want the house rewiring.
I changed a faulty metal class1 fitting for a pendant (to her disapproval) , have advised to replace the other remaining fittings cant do no more.
 
Part number would be K1186WHI

I'm guessing it must be the 'shockguard' version, which only makes connection when lamp is fitted.


Edit: That part number isn't one of their shockguard pendants.
 
Last edited by a moderator:
It looks a bit ad hoc I would query it with MK.
I don't think it is. My preferred pendant sets are MK, they've always been like this as long as I've been using them. I like the terminals in them.

Here's another lampholder, don't know what brand. I bought it a while back from an online shop for a table lamp repair.

[ElectriciansForums.net] Is a standard Pendant a Class 2 fitting?
 

Reply to Is a standard Pendant a Class 2 fitting? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
291
I find with these so called 'class 2' metal light fittings which are basically class 1 fittings with a crappy supposedly double insulated joint...
    • Funny
    • Like
Replies
20
Views
3K
  • Question
i saw a good description recently where it said that BS7671 is directly referenced in other legislation which I haven’t seen before and it better...
Replies
20
Views
3K
  • Question
A quick check on the typical let-through curves for the Hager B6 MCB has around 6,000 A2s at 3kA PFC so adiabatic would be 0.54mm using k=143 from...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks