Hi All

I’m presuming a standard pendant is a class 2 fitting as the earth terminals are not needed as it’s a plastic fitting and it only has an insulated 2 core going to the actual ‘lamp part’.

Am I correct in thinking this?

The reason I ask is Screwfix have replied to someone’s question that it is a class 1 and requires an earth? Even though it is only used to loop in/out.

Can anyone clarify this for me.

Thanks E4F9170E-4F95-44C1-B671-7ACCE8B5BBFF.jpegA7B978CF-7918-4E13-8D37-39AFE2E772C6.jpeg
 
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.
 
I'd say that the earth terminal within an insulated pendant base is purely there as either a parking or loop terminal depending on the wiring method and serves no other purpose with regard to the fitting. So in a situation where the lighting cable has no cpc and rewiring just isn't an option at that time then the pendant is a far safer and satisfactory alternative to a metal Class 1 fitting.

Agree. But it's not classified as class II.
 
For flip's sake, that's my post blown out of the water. Cheers!

But then, hold on - that's only the holder part. The assembly is not class 2.
just checked a BG pendant and it has no symbols or markings to help us.
and for the first time ever, i have actually read the enclosed instruction leaflet and it also has no useful information.
 
From definitions:

Class II equipment. Equipment in which protection against electric shock does not rely on basic insulation only, but in which additional safety precautions such as supplementary insulation are provided, there being no provision for the connection of exposed metalwork of the equipment to a protective conductor, and no reliance upon precautions to be taken in the fixed wiring of the installation (see BS EN 6 1140).
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Is a standard Pendant a Class 2 fitting?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
66
Unsolved
--

Advert

Thread statistics

Created
bilabonic,
Last reply from
Risteard,
Replies
66
Views
9,554

Advert

Back
Top