See post number 15This is what I found & only on non Pme supplies
Yes, it is in the current standard (18th edition amd 2.)This is new to me too is the reg present in the latest amendment books
How far away is the greenhouseClient wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
There’s a duct into the greenhouse, which comes from a external power point, so maybe rubber cablingHow far away is the greenhouse
Are you planning on using swa ?
Except Pme suppliesWhy TT, just run a 1.5mm^2 swa including the armour as CPC and bonding and it meets the regs.
Cheapest option
It’s in the new book but without looking @ the blue book I’m pretty sure it’s in there too.If that is the new book I did wonder if it applied to all TN systems.
It is there but is now amended.It’s in the new book but without looking @ the blue book I’m pretty sure it’s in there too.
Cheers…can’t get to my book yet…having a new bathroom fitted, the house upside down @ the momentIt is there but is now amended.
No not except PME, it is except where PME conditions apply.Except Pme suppliesView attachment 96674
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.No not except PME, it is except where PME conditions apply.
You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.
The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.
In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!
This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
Definitely not apply to TNSThis has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
Where do you get the 10mm from?I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
I understood you to mean all tn conditions applicable to electrical installations beyond the utility supply point when I answered yes i.e. the area covered by the wiring regs; but fair enough, within the utility network the content of the wiring regs is not necessarily applicable.This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
10mm on a TNCS/ PME supply where the Neutral size is 35mm <Where do you get the 10mm from?
If that's from table 54.8 or 544.1.1 then as per your wording - those figures are "except where PME conditions apply "
Where do you get this from?10mm on a TNCS/ PME supply where the Neutral size is 35mm <
Yea I knowWhere do you get this from?
If it's table 54.8 or 544.1.1 then as per your wording - those figures are "except where PME conditions apply "
Yea I know
Which would mean in accordance with 544.1.1 main bonding in sub-buildings could be sized at 50% of the conductors to that building or 6mm^2 whichever is the greater.Your last sentence is exactly correct
I shall be installing a TT System with the appropriate MPBCWhich would mean in accordance with 544.1.1 main bonding in sub-buildings could be sized at 50% of the conductors to that building or 6mm^2 whichever is the greater.
Just running a 1.5 or 2.5 SWA from the cu to this outlet and bonding the metal frame via 6mm^2 from the swa (+cpc if a 3rd core used) would be completely compliant with the minimum expense.