Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
This is what I found & only on non Pme supplies
 

Attachments

  • [ElectriciansForums.net] Power point in external glasshouse
    70BF045C-E71C-4B58-89A0-B1C9FB309522.jpeg
    384.6 KB · Views: 41
Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
How far away is the greenhouse
Are you planning on using swa ?
 
No not except PME, it is except where PME conditions apply.


You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.


The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.

In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!

This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
 
No not except PME, it is except where PME conditions apply.


You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.


The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.

In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!

This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
 
This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
 
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
Where do you get the 10mm from?

If that's from table 54.8 or 544.1.1 then as per your wording - those figures are "except where PME conditions apply "
 
This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
I understood you to mean all tn conditions applicable to electrical installations beyond the utility supply point when I answered yes i.e. the area covered by the wiring regs; but fair enough, within the utility network the content of the wiring regs is not necessarily applicable.
 
Yea I know

So if you believe that the PME note means that in any case where a PME is used to supply a property, the values in 54.8 and 544.1.1 are not correct , just where do you get the correct size from?

Wouldn't this be a glaring omission from the regs? - inability to size bonding if it's supplied via PME.


Or should we understand that "where PME conditions apply" refers to those situations where the Neutral and earth are combined (CNE) forming part of the PME configuration.

In which case, once they have been split at the service head then 54.8 and 544.1.1 apply in terms if bonding size.
 
Your last sentence is exactly correct
Which would mean in accordance with 544.1.1 main bonding in sub-buildings could be sized at 50% of the conductors to that building or 6mm^2 whichever is the greater.

Just running a 1.5 or 2.5 SWA from the cu to this outlet and bonding the metal frame via 6mm^2 from the swa (+cpc if a 3rd core used) would be completely compliant with the minimum expense.
 
Which would mean in accordance with 544.1.1 main bonding in sub-buildings could be sized at 50% of the conductors to that building or 6mm^2 whichever is the greater.

Just running a 1.5 or 2.5 SWA from the cu to this outlet and bonding the metal frame via 6mm^2 from the swa (+cpc if a 3rd core used) would be completely compliant with the minimum expense.
I shall be installing a TT System with the appropriate MPBC
 

Reply to Power point in external glasshouse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2
Replies
31
Views
2K
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
406
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
1K
  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks