Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
Why TT, just run a 1.5mm^2 swa including the armour as CPC and bonding and it meets the regs.

Cheapest option
Except Pme supplies
0F0A21A5-0FCD-4346-9078-FBA7933B0EE3.jpeg
 
Last edited by a moderator:
No not except PME, it is except where PME conditions apply.


You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.


The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.

In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!

This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
 
No not except PME, it is except where PME conditions apply.


You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.


The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.

In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!

This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
 
This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
 
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
Where do you get the 10mm from?

If that's from table 54.8 or 544.1.1 then as per your wording - those figures are "except where PME conditions apply "
 
This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
I understood you to mean all tn conditions applicable to electrical installations beyond the utility supply point when I answered yes i.e. the area covered by the wiring regs; but fair enough, within the utility network the content of the wiring regs is not necessarily applicable.
 