Except Pme suppliesWhy TT, just run a 1.5mm^2 swa including the armour as CPC and bonding and it meets the regs.
Cheapest option
It’s in the new book but without looking @ the blue book I’m pretty sure it’s in there too.If that is the new book I did wonder if it applied to all TN systems.
It is there but is now amended.It’s in the new book but without looking @ the blue book I’m pretty sure it’s in there too.
Cheers…can’t get to my book yet…having a new bathroom fitted, the house upside down @ the momentIt is there but is now amended.
No not except PME, it is except where PME conditions apply.Except Pme suppliesView attachment 96674
I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.No not except PME, it is except where PME conditions apply.
You should not be applying PME as the CNE will have been split at the header into L, N & E. You should never combine the N & E within the installation.
The note re except where PME conditions apply, was there over several versions of the regs, we would still apply the 50% or min 10mm^2 rule.
In fact there is no sizing for bonding within the (wiring) regulations where PME does apply!
This is usually determined by the utility themselves, and is often 50% or min 16mm^2 for customer service points, and generally 32mm^2 within the network (eg SNE sheath to CNE) even if its to one customer.
Definitely not apply to TNSThis has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
Where do you get the 10mm from?I don’t intend to combine N & E..never have…For me it’s gonna be a TT system @ the greenhouse.
Also the 10mm MPBC would apply if using the DNO earth
I understood you to mean all tn conditions applicable to electrical installations beyond the utility supply point when I answered yes i.e. the area covered by the wiring regs; but fair enough, within the utility network the content of the wiring regs is not necessarily applicable.This has become somewhat confused I asked in #22 if this applied to all TN systems and whilst TN-C-S does not necessarily mean PME I was answered yes it does but it doesn't?
10mm on a TNCS/ PME supply where the Neutral size is 35mm <Where do you get the 10mm from?
If that's from table 54.8 or 544.1.1 then as per your wording - those figures are "except where PME conditions apply "
Where do you get this from?10mm on a TNCS/ PME supply where the Neutral size is 35mm <