Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.
The key part is the second paragraph:
"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."
(Min 6mm^2; max needed 25mm^2 of course)
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.
You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm
I have heard of this new Reg but not perused it does it apply to all TN systems.No, it's not the MPBC, it's extraneous conductive part in a remote building therefore the bonding size is dependent upon the circuit to that building.
I have heard of this new Reg but not perused it does it apply to all TN systems.
This is new to me too is the reg present in the latest amendment booksI have heard of this new Reg but not perused it does it apply to all TN systems.
See post number 15This is what I found & only on non Pme supplies
Yes, it is in the current standard (18th edition amd 2.)This is new to me too is the reg present in the latest amendment books
How far away is the greenhouseClient wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
There’s a duct into the greenhouse, which comes from a external power point, so maybe rubber cablingHow far away is the greenhouse
Are you planning on using swa ?