Fun EICR at an HMO today, which was installed new 5 years ago (not particularly well!)
Lots of niggly things that I'll sort, but in the kitchen cupboards were two unswitched sockets which confused me for a while.
Turns out they are connected to the lighting circuit, switched by their own switch by the door - apparently originally for pelmet lighting that was never installed.
I'll likely blank them off anyway, but was thinking about how I'd code it and swinging between a C2 and a C3.
Everything is RCD protected, so that's not an issue. 6A breaker should trip fast enough to avoid any long term overload of the cable (1.5mm)
In purely terms of actual or potential danger, where would others put it? It's clearly bad workmanship and something that should never have been installed 5 years ago, and there's an argument for putting C2 just to ensure it gets changed, but that's rather against the spirit of the codes - Is there enough potential danger to reach a C2..
Lots of niggly things that I'll sort, but in the kitchen cupboards were two unswitched sockets which confused me for a while.
Turns out they are connected to the lighting circuit, switched by their own switch by the door - apparently originally for pelmet lighting that was never installed.
I'll likely blank them off anyway, but was thinking about how I'd code it and swinging between a C2 and a C3.
Everything is RCD protected, so that's not an issue. 6A breaker should trip fast enough to avoid any long term overload of the cable (1.5mm)
In purely terms of actual or potential danger, where would others put it? It's clearly bad workmanship and something that should never have been installed 5 years ago, and there's an argument for putting C2 just to ensure it gets changed, but that's rather against the spirit of the codes - Is there enough potential danger to reach a C2..