If my math below is wrong, please point it out
@TechyTim
1) The CT lead is fine, we've used one of those CT's for years, it doesn't get moved around like an earphone.
2) It is possible, you only need to monitor the main incoming lead before the CU and before the PV, so it doesn't matter wether the PV is wired via henley blocks or into the CU, it monitors that actual incoming / export with a single CT (just like CT meters do) - never found a place yet where there isn't room to put a CT on the incoming
3) Time will tell
4) Yes Tim, however, this isn't an 'on/off' contrioller it's proportional, your isn't -
From your site, "When the sun is shining strongly and the power generated by the PV panels exceeds 1.5kW or 2.5kW (depending on model), the feed to the Immersion Heater will be switched on at the consumer unit." i.e. it takes no account of base load, or other units that may be consuming power
Just so Tim doesn't get accused of selling on the forum, I'll post the link to his product
.:Energyfactor UK:. - Energy consultancy
"A simple low cost controller which switches on the immersion heater when the sun is shining and your PV panels have sufficient output to give low cost hot water"
That's the point - It's horses for courses and pays ya choice.
If you want a controller that specifically monitors wether power that would be exported is available and you want to proportionally control the output to that heater without changing the element and NOT to heat it when the base load is consuming all generated power, then its ÂŁ400, if you want a switch based on what you are generating its Tim's ÂŁ200 or other similar ebay models.
The real savings maths have to take into account trigger point, base load etc.
Taking four simple examples, and two scenarios:
1) Proportional control, with a 200W trigger point, dumping all load to heating elements
2) 1.5kW trigger from Tim, dumping to a 1.5kW heating element
2) 3kW trigger from Tim, dumping to a 3kW heating element
2) 1.5kW trigger from Tim, dumping to a 1kW heating element
Scenarios
A) No base load (never the real case)
B) 600W base load
With the 600W base load, examples 2 and 3 will of course mean that some electricity will actually be imported as the base load needs to be supplied, so that results in an import cost, hence example 4, effectively allows for a 500W base load.
Best 'saving' is from a proportional control with no base load, next best is using a 1.5kW trigger with a 1.5kW load with no base load on a 4Kwp system.
As far as ROI is concerned, the MOST money will be saved by the proportional control, and the key thing is that both have an payback period in the region of 2 -3 years allowing for the install costs - ALL so long as you can use the excess power.
Figures attached are based on the 5 minute data from the real output of a system on 28th June (its as good as any day
)
View attachment 13422View attachment 13423View attachment 13424