The current draw will remain the same whether it's a 13amp fuse or a 16amp mcb.
No it will not. A double socket is rated to draw 20A (it can draw 26A), yet they are are ubiquitous on rings. That is one point off a final ring. A 16A MCB, one point off a final ring, draws less than a common double socket.
 
No it will not. A double socket is rated to draw 20A (it can draw 26A), yet they are are ubiquitous on rings. That is one point off a final ring. A 16A MCB, one point off a final ring, draws less than a common double socket.

But that's not what you said is it John.
 
Any advantage, no matter how small, would make a DP superior to SP.
One advantage would be safe local isolation.
There are other advantages, but I really can't be bothered arguing about the obvious.
On the Continent all breakers in the CU are dp. It is abundantly obvious dp is superior.
 
No it will not. A double socket is rated to draw 20A (it can draw 26A), yet they are are ubiquitous on rings. That is one point off a final ring. A 16A MCB, one point off a final ring, draws less than a common double socket.
If you plug a 3 amp load into a 100 amp circuit, it will draw 3 amps

If you plug the same 3 amp load into a 200 amp circuit, it will draw exactly the same.
 
No it will not. A double socket is rated to draw 20A (it can draw 26A), yet they are are ubiquitous on rings. That is one point off a final ring. A 16A MCB, one point off a final ring, draws less than a common double socket.
The outlet doesn't draw anything, it's the appliance that draws the current.
 
If you plug a 3 amp load into a 100 amp circuit, it will draw 3 amps

If you plug the same 3 amp load into a 200 amp circuit, it will draw exactly the same.
A double socket's max load is rated to draw 20A (it can draw 26A if two 13A appliances are plugged in). On a ring that is say a 20A thru that socket and that point on the ring. As I wrote that is one point off a final ring. A 16A MCB, is one point off a final ring, drawing less than a common double socket on a ring. So to those who say a ring only takes 13A, not so. Even with no 16A MCB off a ring, far more than 16A can be drawn from one point.
 
Last edited:
A double socket's max load is rated to draw 20A (it can draw 26A if two 13A appliances are plugged in). On a ring that is say a 20A thru that socket and that point on the ring. As I wrote that is one point off a final ring. A 16A MCB, is one point off a final ring, drawing less than a common double socket on a ring. So to those who say a ring only takes 13A, not so. Even with no 16A MCB off a ring, far more than 16A can be drawn from one point.
Well done, some very useful information that I'm sure hardly anyone knew.
 
A double socket's max load is rated to draw 20A (it can draw 26A if two 13A appliances are plugged in). On a ring that is say a 20A thru that socket and that point on the ring. As I wrote that is one point off a final ring. A 16A MCB, is one point off a final ring, drawing less than a common double socket on a ring. So to those who say a ring only takes 13A, not so. Even with no 16A MCB off a ring, far more than 16A can be drawn from one point.

I don't think anyone on here is in any doubt that a double socket on a ring can draw more than 13 Amps. This is very basic stuff.

You do realise this is a forum for electricians right? I think you are underestimating the knowledge and experience of people considerably.

Or you're just trolling John.
 
I don't think anyone on here is in any doubt that a double socket on a ring can draw more than 13 Amps. This is very basic stuff.

You do realise this is a forum for electricians right? I think you are underestimating the knowledge and experience of people considerably.

Or you're just trolling John.
Some of the comments indicate a clear lack of understanding. Many think a point off a ring cannot draw more than 13A. When final rings were formulated they only had single 13A socket outlets. This is not is so, as a max' 16A appliance can be taken taken off a ring. Some here think a sp breaker has no advantage over a dp. No kidding. This thread casts doubts of the technical understanding of many contributors, although some are good.
You are confused having the wrong person.

What is evident is how many take matters to a personal level, or engage in ad hom' attacks on this forum rather than sticking to the technical issues at hand. A sign of insecurity for sure.
 
Last edited:
Status
Not open for further replies.

Reply to Immersion fuse or MCB? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
The relay worked as expected. A link was needed between L and L1. Only problem was the neutral terminal screw didn't tighten up, so he is...
Replies
17
Views
3K
  • Question
If it’s not possible to supply elsewhere then connect to the IH circuit, keep him happy label it… after all its a radial circuit dedicated for...
Replies
7
Views
3K
  • Question
I received the latest Guidance Note 4 - Protection Against Fire yesterday. My first observation is it's the first guidance note I've ever known...
2
Replies
43
Views
6K
  • Question
But a plug ‘top’ BS1362 fuse is not protecting fixed wiring is it, so perhaps not a good analogy.
2
Replies
35
Views
8K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks