Is RCD needed at both ends of armour feed to outbuilding | Page 4 | on ElectriciansForums
Guest viewing is limited

Discuss Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Never said I would have a rcd at both ends, either a mains switch at mains with a local rcd in garage or rcd at mains with main switch in garage. So there would only ever be one rcd. Am no fool so please don't make out or judge my competence engineer54 I several years experience from bms, hvac inverter drives, trend plc programming from running a 56 flat domestic installation. I am no dummy but far from the best and always look to learn more
 
Never said I would have a rcd at both ends, either a mains switch at mains with a local rcd in garage or rcd at mains with main switch in garage. So there would only ever be one rcd. Am no fool so please don't make out or judge my competence engineer54 I several years experience from bms, hvac inverter drives, trend plc programming from running a 56 flat domestic installation. I am no dummy but far from the best and always look to learn more

No one is questioning your competence mate, just that of the OP's
 
If you had two 30mA RCDs at each end of your sub-main, there is no guarantee which one would trip first, or even both would trip together, this means they won't discriminate with each other.

I usually prefer to have the RCD local (in the out building), as it is more convenient to re-set if it trips, instead of having to walk (possibly in darkness) some distance away to re-set.

Really makes you wonder doesn't it, and this is after 2 years of practicing on paying customers installations!! Another example of why there is no such thing as a Domestic Installer!!
 
Never said I would have a rcd at both ends, either a mains switch at mains with a local rcd in garage or rcd at mains with main switch in garage. So there would only ever be one rcd. Am no fool so please don't make out or judge my competence engineer54 I several years experience from bms, hvac inverter drives, trend plc programming from running a 56 flat domestic installation. I am no dummy but far from the best and always look to learn more

Then don't act like one then, because i had you mixed up with the OP!! lol!!
 
I had him mixed up with the OP too lol
I had to quickly edit a previous post, are we answering two peoples queries here ?
 
I was thinking like hang on am getting butchered here for making a observation, was nice testing the water though as I am new to this forum
 
I was just stating that a napit assessor had told me to when doing a garage or outbuilding installation u had to use a earth rod for the earth in the garage, I would of normally brought a 3core swa across and used a core for the earth. I just gave a brief description of how I would of done the job, then all hell broke loose
 
Well it proved both NIC and Napit talk ballocks lol, no doubt Elecsa do too!

I don't think I have ever asked them a question, most stuff I do is not part P anyway, I only keep it on for when my usual stuff goes quiet, so long as it pays for itself I keep it going, into my 4th year now, and with it being watered down recently it nearly didn't get renewed this year at all.
 
I was just stating that a napit assessor had told me to when doing a garage or outbuilding installation u had to use a earth rod for the earth in the garage, I would of normally brought a 3core swa across and used a core for the earth. I just gave a brief description of how I would of done the job, then all hell broke loose

If my assessor pulled me up on a job like this I would hand him the regs book and the pile of GNs and tell him to explain to me where I had done anything wrong, I would like to bet him next years fees he couldn't lol
 

Reply to Is RCD needed at both ends of armour feed to outbuilding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
699
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top