Hi I've done a Ze test on a TNS system and it's come back as 0.14 ohms is this reading ok as the max is 0.8 is there not a min amount you can have thanks
Discuss Ze external earth loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Am always a little suspicious when questions like this pop up from new members during one of Glen's bans!
1 week. for posting a picture of a pair of ----. wonder if this picture of a single --- will get me a ban.
View attachment 22063
He isn't banned again is he!
Hi I've done a Ze test on a TNS system and it's come back as 0.14 ohms is this reading ok as the max is 0.8 is there not a min amount you can have thanks
1 week. for posting a picture of a pair of ----. wonder if this picture of a single --- will get me a ban.
View attachment 22063
View attachment 22072
Naaa it would be too obvious if I posted a picture of a fine upstanding cockerel.
better watch it, geordie, she'll be running off with a cockney next.
That's what you think ....... I know she hates Cockneys, so why the Hell she watches Eastenders all the time I don't know!!
Eng,Just means your damn near a local DNO distribution substation... lol!! Start worrying when you're getting values 00.4 ohms!! lol!!
Eng,
Do you mean 0.04 Ohms or even .004 ohms? (thats a lotta raisins)
Eng is still in Cyprus on hols till the 10th, sippin the oozo (spelling?).:17:
And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.
Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V
250-35 = 215 V, very close to the 216.2 V minimum(230-6%)