S

Simon Hall

Hi I've done a Ze test on a TNS system and it's come back as 0.14 ohms is this reading ok as the max is 0.8 is there not a min amount you can have thanks
 
reading is fine. there is no minimum specified. damn good earth. i frequently get around 0.2.
 
Am always a little suspicious when questions like this pop up from new members during one of Glen's bans! :)

He isn't banned again is he!
 
Hi I've done a Ze test on a TNS system and it's come back as 0.14 ohms is this reading ok as the max is 0.8 is there not a min amount you can have thanks

Just means your damn near a local DNO distribution substation... lol!! Start worrying when you're getting values 00.4 ohms!! lol!!
 
And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.
 
And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.

Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V

250-35 = 215 V, very close to the 216.2 V minimum(230-6%)
 
Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V

250-35 = 215 V, very close to the 216.2 V minimum(230-6%)

Eh???? I think you need to have a think about that.
 

Reply to Ze external earth loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
Replies
22
Views
897
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
161
  • Question
(2.4-0.4)×1.2+0.4 = 2.8ohms
Replies
4
Views
1K
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks