And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.

Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V

250-35 = 215 V, very close to the 216.2 V minimum(230-6%)
 
Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V

250-35 = 215 V, very close to the 216.2 V minimum(230-6%)

Eh???? I think you need to have a think about that.
 
Just in case I'm misunderstanding you...walk through it once more.

Well on a single phase system whats the mimimum voltage.

So for a 100 amp supply, assuming a current of 100amps 35 volts will be dropped in the supply.

So if at Tx terminals we have 250v then and 35 v dropped across supply then only 215 v is supplied at the consumers service head
 

Reply to Ze external earth loop impedance in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Good thinking - the other side of that is my garage and also where the gas comes in so probably quite a tidy solution if it comes to it!
2
Replies
22
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top