Eng,Just means your damn near a local DNO distribution substation... lol!! Start worrying when you're getting values 00.4 ohms!! lol!!
Eng,
Do you mean 0.04 Ohms or even .004 ohms? (thats a lotta raisins)
Eng is still in Cyprus on hols till the 10th, sippin the oozo (spelling?).:17:
And, just to point out something else.... there's not really such a thing as a maximum Ze value, either, as they don't officially exist. Neither BS7671 nor ESQCR contain the mythical figures of .35 and .8 for TN systems so the DNO's are quite at liberty to deliver as they wish. The only which IS set in stone is that circuit max Zs figures have to be achieved.
Your right to a point, though take PME, their is a legal limit with regards volts. So Tx set to 250 V and a 100 amp supply PME 0.35. So 100 x .35 = 35 V
250-35 = 215 V, very close to the 216.2 V minimum(230-6%)
Eh???? I think you need to have a think about that.
Why, whats wrong with it
Eng,
Do you mean 0.04 Ohms or even .004 ohms? (thats a lotta raisins)
Just in case I'm misunderstanding you...walk through it once more.