Chr!s
-
Indeed. But where in that loop are you taking your A point to support a % vd?
At the service Head, Line and Neutral, so A and B
You're taking it at the entry point of our practical load, which means it's being referenced to zero at the end of that load
Why is it being referenced to Zero, is that the potential you think the neutral will be at.So based on your assumption then no current flows int the neutral? Its simple ohms law, you have a current you have an impedance therefore you have a voltage.
- otherwise, we end up in a muddle of trying to define a %'ge as 245/245 which is meaningless. Hence, what follows after the connection to the neutral point is irrelevant.
No its not! Lets start with an open PEN, what voltage would you expect at the PME LINK assuming no extraneous conductive parts for current to flow?
Now lets add a impedance to the the neutral 100 ohms, whats the voltage now at the head, then do it at 10 ohms 1, 0.1 ... Whats happening to the Voltage on the neutral at the service head?
Besides, WPD around here will allow a PME connection to be as high as a TN-S at .85 So now work that one out at your 100A as before. 85VD at source? I think not.
WPD are my DNO, and if they are putting 100 amp supply's on a weak supply like that there in for a lot of trouble. Im not aware of 100 amp supply's being offered on weak systems like that!!
I know they offer PME on supply's slightly above 0.35, but you will get an 80/60 amp supply.