I have just changed a CU. I did find a neutral - earth fault prior to the change so I thought I would probably have a tripping RCD.. which I did!

My dilema is how do I proceed with the paperwork?

I'm going back tomorrow morning to do all of the testing and I shall give the required certificates (with a note on regarding neutral/earth fault on downstairs lights), but I get the feeling the chap is going to hunt for the fault himself, the reason being it will require the floorboards being taking up and he doesn't want to incur anymore cost (fault is in a junction box(s), under the floorboards that someone has kindly wired all the downstairs lights from - took me a while to figure this out!)

The main point being that the work is notifiable, but I cant notify it if it still has faults! How do I proceed?

I realise I should have perhaps corrected the fault before the CU change, but the chap just wanted the new CU in and due to my inexperience I wasn't sure if the new CU would trip!

Cheers...
 
I've got a cu change next Tuesday which fingers crossed will be ok as it appeared to test out ok, but another that I still have to do had a couple of faults hich really need to be resolved first.

I think all I'd say is you should perhaps have fixed the fault before changing the cu, I know it's not always the way we think, but it tends to make things less complicated.
 
How is the lighting circuit on if you haven't fixed the fault?
On fixing the fault - let the guy make a start, pulling the boards up, exposing the Jbs, then you should be able to find and fix in no time.... Stick to your original price and put the extra time spent as a learning curve.

Ste
:)
 
Evening all..

I have just changed a CU. I did find a neutral - earth fault prior to the change so I thought I would probably have a tripping RCD.. which I did!

My dilema is how do I proceed with the paperwork?

I'm going back tomorrow morning to do all of the testing and I shall give the required certificates (with a note on regarding neutral/earth fault on downstairs lights), but I get the feeling the chap is going to hunt for the fault himself, the reason being it will require the floorboards being taking up and he doesn't want to incur anymore cost (fault is in a junction box(s), under the floorboards that someone has kindly wired all the downstairs lights from - took me a while to figure this out!)

The main point being that the work is notifiable, but I cant notify it if it still has faults! How do I proceed?

I realise I should have perhaps corrected the fault before the CU change, but the chap just wanted the new CU in and due to my inexperience I wasn't sure if the new CU would trip!

Cheers...
so it must have come as a pleasant surprise then when...holy of holys..:..this happened
 
I'm not understanding this at all?? If you found that you had a problem prior to changing the CU why didn't you inform the customer at that time?? It's now down to you to sort the problem out, whether you can now charge him for any extra work is another matter. But you can't seriously be thinking of walking away from this installation knowing there is a fault on the installation surely??
 
this is just rubbish...

this OP IS NOT COMPETENT!!

sorry hippy but i`v read loads of your posts and i wouldn`t let you any where near an electrical installation...

for the life of me:nonod:...
 
Last edited by a moderator:
Agreed.

You shoulda informed the client before hand, it's a regular occurance what's happened to be honest - but when you tell mr.smith that the nice new cu will be cutting out because he's got a fault 99% of the time they agree to the additional works. If they don't consent to it, write up a little contract stating that his electrics wont work once you've done the job get him to sign it and walk away laughing.

However...you're probably gonna have to sort this out for free. Remember next time, correct before the CU swap OR at least inform the client. You can fill in the EIC if you really want too, but if someone with a trained eye gets hold of it you're going to look rather silly - as readings will be unacceptable.

Correct the fault, then issue the paperwork. Only option im afraid. Best of luck!
 
this is just rubbish...

this OP IS NOT COMPETENT!!

sorry hippy but i`v read loads of your posts and i wouldn`t let you any where near an electrical installation...

for the life of me:nonod:...

Haha, im impressed glenn ... you held your true feelings in for at least 4posts, but then it came blurting out coz ya couldn't help ya'sen could ya! lol

:)
 
I've got a cu change next Tuesday which fingers crossed will be ok as it appeared to test out ok, but another that I still have to do had a couple of faults hich really need to be resolved first.

I think all I'd say is you should perhaps have fixed the fault before changing the cu, I know it's not always the way we think, but it tends to make things less complicated.

Thanks UK, you're quite right... feel quite silly.

How is the lighting circuit on if you haven't fixed the fault?
On fixing the fault - let the guy make a start, pulling the boards up, exposing the Jbs, then you should be able to find and fix in no time.... Stick to your original price and put the extra time spent as a learning curve.


:)

quite right too.. Thanks

i dont know if i really should reply to this...

Glenn, theres no way on this earth that you would not be able to reply to this thread!!

I'm not understanding this at all?? If you found that you had a problem prior to changing the CU why didn't you inform the customer at that time?? It's now down to you to sort the problem out, whether you can now charge him for any extra work is another matter. But you can't seriously be thinking of walking away from this installation knowing there is a fault on the installation surely??

Thanks for your blunt, yet correct advice E54, I wont be charging him for the extra work.

this is just rubbish...

this OP IS NOT COMPETENT!!

sorry hippy but i`v read loads of your posts and i wouldn`t let you any where near an electrical installation...

for the life of me:nonod:...

I'm sure you'll be able to do the work yourself Glenn, If you really need a hand thats fine but just give a go yourself... you'll be fine! ;)

Agreed.

You shoulda informed the client before hand, it's a regular occurance what's happened to be honest - but when you tell mr.smith that the nice new cu will be cutting out because he's got a fault 99% of the time they agree to the additional works. If they don't consent to it, write up a little contract stating that his electrics wont work once you've done the job get him to sign it and walk away laughing.

I kind of got that impression, I did speak to an electrician friend, who said just change it! Also another spark was on site who said this happened to him alot! No excuse for me to get into that habit though!

However...you're probably gonna have to sort this out for free. Remember next time, correct before the CU swap OR at least inform the client. You can fill in the EIC if you really want too, but if someone with a trained eye gets hold of it you're going to look rather silly - as readings will be unacceptable.

Yep

Correct the fault, then issue the paperwork. Only option im afraid. Best of luck!

Cheers Mark

 
You need to include this caveat on your quote/estimate:

"NB: Should the testing of the existing circuits find any faults there may be additional charges. Such additions would be discussed with you at the time."

So did you leave them without lights then?
 
You need to include this caveat on your quote/estimate:

"NB: Should the testing of the existing circuits find any faults there may be additional charges. Such additions would be discussed with you at the time."

So did you leave them without lights then?

that's all well and good, but he needs to ACtually tell them of any existing faults which is where he let himself down!
 
You need to include this caveat on your quote/estimate:

I shall definitely be doing that next time!

"NB: Should the testing of the existing circuits find any faults there may be additional charges. Such additions would be discussed with you at the time."

So did you leave them without lights then?

He has not moved into the house yet, but yes there were no downstairs lights, however sockets were on so light could have be plugged in.


I returned to the house this morning and found the following JB's under the floorboards in the bathroom:

[ElectriciansForums.net] Consumer unit change with a fault!

No earth sleeving and one was touching the neutral terminal.

VERY glad I found the problem, but embarrassed not to have hunted for it before changing the CU, no charge.. Lesson learnt. :redface:
 
564 posts
Member since 2011

Still a Electrical Trainee

I'm sorry HHD, in the past you've asked how to wire a doorbell!

No one in their right mind would let you loose on the public.

I've said to much already.
 
this is just rubbish...

this OP IS NOT COMPETENT!!

sorry hippy but i`v read loads of your posts and i wouldn`t let you any where near an electrical installation...

for the life of me:nonod:...

And you'll read alot more of them too Glen. Unlike the many new members who you have bullied and who will now be too afraid to ask any further questions It doesn't bother me.
 
I returned to the house this morning and found the following JB's under the floorboards in the bathroom:

View attachment 22848

No earth sleeving and one was touching the neutral terminal.

VERY glad I found the problem, but embarrassed not to have hunted for it before changing the CU, no charge.. Lesson learnt. :redface:

Good feedback mate and 10/10 for being honest.

Skills that are sadly lacking on this forum these days.:juggle2:
 
Tony beat me to the door bell bit.
This shows whats wrong with the system nowadays and the danger the public are in.
This particular Electrical Trainee posted for answers about wiring a door bell, then doing a pir, now cu change problems.
All of which could be accepted from an apprentice but this guy is loose on the public.


Boydy
 

Reply to Consumer unit change with a fault! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok I’ll try this when I’m down
Replies
4
Views
285
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
445
davesparks
D
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
635
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks