When testing (30ma RCD) to (BSEN-61008), am I correct In thinking you record the lowest values & not the highest value reading obtained @ x 5 In, for the schedule of test results, for example.
X 1/2 In-No trip
X 1 In-0-180-Under 300-ms
X 5 In-0-180-Under 40-ms
Check test button for operational...