Thanks Biff, but as i said bonding to gas and main earthing comes from the head, and all seals are in place, otherwise it would be so temting is in it?
As per title, urgent advice needed.
I have an ELECSA assessment tomorrow for the installation work and condition reporting. I am fine with EICRwork to show, but the person with whom I agreed that her install by me will be checked tomorrow, called me at 3pm today that she will not going...
Thanks everyone, but from post 8 I did realised my mistake, and all relevent regs been noted. .i think this thread can remain as history now. thanks again.
Al
Thanks everyone for the replies, obviously i got that wrong, i dont remember where did that came from, i did reed that somewhere, probably that was a guide or recomendation and not the regs.
I need to look in regs book more offen then.
thanks again everyone
Hello everyone and HNY.
I need clarification on this:
I been asked to change the fuse board in commercial premises, it is a sub main SP board in a basement area. The earthing cable/cpc to board is the armor of SWA cable, all circuits to the accessories has the cpc via metal conduit. I had a...
Ze(L to E) -Knob 1 L-E, knob 2 Z or Zmax if you want the tester to remember your highest reading. Plug the test leads in + red and - green in the tester. PEFC is displayed at the same time.
Ze(L to L or L to N) -Knob 1 L-L/L-N, knob 2- Z,test leads plug in - red and blue on tester.PSCC will...
If you want for the regs on that conduit, look for conduit support spacings, looks like you have about 2 m run with no supports(no compliant), then white pvc is not good in sunlight(not sure about regs on this one), and then I see this conduit being a good support for some numpty doing pullups.
thanks for reply, i dont think it is PILC, there is no lead sheath, probably it is more like split concentric as you say becouse of the fine copper strands visible on the sheath, I promise to do pics tomorrow.
I am seeing it coming from the sheath at the intake, which is a supply for them containers only, nothing else. It comes in the made for that purppose pillar/box 15 m away from the main container where the main board will be. Not sure about the incoming cable, the only thing I good see that it...
Tested today again. Ze(E to L)=0.26 ohms, Ze(L to N)=0.16 ohms. Loks TNS to me...??? Sorry no pics again, cant get used to the new phone, too bussy.....
How can you have TN-C-S from the sheathing?
Thats what I trying to work it out,its just somene pointed out to it stright away
What's the problem when Ze is 0.25?
I know, looks good to me.
Have you measured Zn/PSCC?
Will do first think this morning,was too busy yeasterday digging...
Thanks Marvo, I understand that, its just I want someone to tell me that TN-C-S earthing comes from sheathing too sometimes,cos I never come acros, normaly it is split at the head, which is not the case here. thanks
I know that, if that is TN-C-S,( bearing in mind lost neutral and stuff)then I need to bang more rods in, and make the TT better then it is , but I want to be 100% sure that it is, thanks.
Hello, I wonder if there is anyone here to help me out. Thanks in advance for the help.
Ok. I am doing electrics on 6 metal containers in community fields( I know, I don’t like them metal boxes too), I got it all under control, but there is little thing what buggers me. I kind of finding...