  1. Ian1981

    Fire Retardant Grommets

    From Hager’s manufacturers instructions Read the cable entry part Extract below For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above. Tests on hager consumer units have indicated that there is no specific need for...
  2. Ian1981

    What is this megger code?

    Have you measured the voltage between line and with the earthing conductor removed from the MET inside the CU?
  3. Ian1981

    What is this megger code?

    The touch voltage to earth has exceeded 50v meaning there’s no earth connection or lack of earth continuity to what you are testing. Modern meters will not allow the test to be performed if this is detected for safety reasons as injecting a test current will raise the unearthed conductor and...
  4. Ian1981

    Dot Dab Plaster wall - 35mm box? Plasterer at odds with electrician

    Ha I miss read your post , you said plasterboard only.
  5. Ian1981

    Dot Dab Plaster wall - 35mm box? Plasterer at odds with electrician

    I’ve never ever seen dot and dab used on ceilings as the plasterboard is fixed to the timbers by screws, dabbing it , it would simply fall down or move.
  6. Ian1981

    Cat 5e cables lashed across ceiling

    The cable in question is cat5 however I would certainly highlight the issue regardless if it had the potential to cause danger through entanglement.
  7. Ian1981

    Reference Method 102

    Install it in conduit which is reference method A and gives the minimum requirement of 20 amps (for 2.5mm) per leg of the ring
  8. Ian1981

    Dot Dab Plaster wall - 35mm box? Plasterer at odds with electrician

    Sounds like the electrician is just being lazy and does not want to chase the boxes in and expects the plasterer to dab out to his boxes , so more work for the plasterer.
  9. Ian1981

    500v IR test shock?

    Then you attach the leads to his -------s
  10. Ian1981

    500v IR test shock?

    Or if your at college, attach the leads to your mates ears
  11. Ian1981

    IR testing on new build

    The simple answer is that the test should have been carried out prior to the loads being fitted in circuit.
  12. Ian1981

    IR testing on new build

    Regulation 643.3.1 does allow the testing of the line and neutral conductors connected together and to the earthing arrangement where appropriate, this falls under chapter 64 which is initial verification and not periodic inspection and testing so it is applicable. This is also echoed in GN3 for...
  13. Ian1981

    500v IR test shock?

    You need to be touching both ends when doing an IR test at 500 v to feel it.
  14. Ian1981

    Calculating inrush current for magnetic ballasts

    Took the words right out of my mouth ?
  15. Ian1981

    Swimming Pool Regs 702

    If the set up at the origin is TT , then 702.410.3.4.3(ii) is irrelevant
  16. Ian1981

    Cat 5e cables lashed across ceiling

    Yes there’s been many a time where we have installed 3 compartment dado trunking, only to find that they have run their data cables in the same compartment as the LV cables, ? ends.
  17. Ian1981

    Cat 5e cables lashed across ceiling

    It’s important to remember the voltage bands that bs7671 deals with, so yes ELV cables will come under bs7671 and are code able under bs7671.
  18. Ian1981

    Calculating inrush current for magnetic ballasts

    Can you use a meter to measure it, a flexible probe or clamp device? I think these are specialist devices but maybe available for rental.
  19. Ian1981

    Phillips or Pozi

    Because pozi are an improvement. what I hate is screwdriver sets that come with Phillips instead of pz2, I never use my PH 2.
  20. Ian1981

    EICR Coding for ring ??

    It will be the total load combined but with built in thermostats for the likes of the grille part, it will never get to that, plus can the grill and the microwave be on together or do that have to work independently?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top