Realistically a pain in the arse to confirm if extraneous if existing and if you have lots of fittings in it which are themselves earthed as they are exposed conductive parts so grid is likely already at earth potential from this.
If it's new you can test it with a IR tester at 500v. If...
Yeah, I've seen that too, sleeved and taped only....With a jubilee around the copper clad to clamp a cpc to!!.... Also seen many in control panels where multiple multi core pyro's brought in through same hole and then pots only fitted........There were some rough old boys out there too back in...
As you've got 2 circuits and 1 is powering 1 light, even if 1mm csa, it will be less than 30% percent of its grouped rating and therefore can be disregarded for the other cables in the group, of which there is one, which is the socket circuit. I really don't think grouping will be an issue. As...
If it has no isolator from DNO and the origin of supply is split then the most comprehensive way would be to complete 2 seperate certs.
It's no different to having a unrestricted and off peak supply at a house, some people do it on two certs and others just add a schedule of inspections and a...
As you already recognise, as your line conductor is 70mm then 35 mm would automatically satisfy the protective conductor sizing requirement of Table 54.7
16mm may well be adequate but this will need to be confirmed by using the adiabatic equation. Will need some more info for this though.
What...
Yeah, definitely. I typo'd too, meant table I1.
If you take any of the mV/A/m values and ÷ 2.4 it will give you the values of (R1 + R2) / Metre in Table I1.
Hi Elliott
RCD would not be a requirement of the unit and you can avoid the additional protection requirement by your install method.
Type B is not recommended due to the inductive load of the compressor in condensor unit. They are almost all inverter driven now though so inrush is not...
Basically the Solis Inverter has Dual MPPT which means it can operate two strings completely independently (2 MPPT as Solis say). As yours are unbalanced it would be detrimental to parallel them together so therefore keep them independent.
I only ever do IR L-L and L-N on initial verification. It is too disruptive and unnecessary for an existing install.
As far as testing periodically, For the breakdown to occur between those it would require 2 faults, which if there is a path between them, almost certainly there is a path to...
At £25 an hour self employed, even if you worked 40 chargeable hours every week, deducted holiday, unpaid sick days, vehicle, other expenses you would not be at 40k. In reality with all the unpaid hours for surveys, quotes etc....even worse. If you got 35k employed you would be better off plus...