  1. Andy-1960

    UK What's 1:500 on a site plan.

    1cm = 500cm so the distance you are measuring is 5 metres
  2. Andy-1960

    Happy Birthday, Andy-1960

    Thank you everyone, much appreciated
  3. Andy-1960

    Help find a part for an old sauna heater

    I think it is a 125 deg safety thermostat and I think,it is the capillary tube you have inadvertently broken off. I doubt you will find an exact replacement but this one is pretty close. https://uk.rs-online.com/web/p/thermostatic-switches/6841208/
  4. Andy-1960

    Joining a cable to be buried in a wall

    Big Clive on YouTube tested these recently and as I recall was not too impressed with the results. The solder does not seem to flow into the connection too well. Think they are ok for low current applications, but that’s about all.
  5. Andy-1960

    3 phase gen set neutral/earth

    If the generator is ok to run, why don’t you run it and measure the voltage between a phase and the earth connection to see if it is a combined neutral earth? If you don’t get a voltage reading you will know that the star point of the winding is floating.
  6. Andy-1960

    Dual socket not working.

    Where in the midlands are you? Maybe a member could pop in and have a look.
  7. Andy-1960

    Generator switch wiring help

    Installing an earth rod is essential when installing any type of generator on a TN-S supply. This is both for your safety and the poor DNO engineer that may be working on the cable feeding your property.
  8. Andy-1960

    Am I missing something

    Switching the neutral is very bad practice as any earth fault on the wiring after the stop button means the contactor will not de-energise when the stop button is pressed and no fuse will blow as it would be a neutral earth fault.
  9. Andy-1960

    3p motor connection

    Bit extreme on a 0.75kw motor!!! 1586603388 Got be Star connected
  10. Andy-1960

    What do I Set the overload to on a soft start

    The setting of soft start unit all depends on how it has been wired and from your photo I can’t tell. Is the soft start wired as a direct on line, I.e 3 wires to the motor or is it inside a delta loop - 6 wires to the motor? If it is 3 wires, you set it to the current rating of the motor plate...
  11. Andy-1960

    BMW F30 REAR LEFT TURN SIGNAL DOESN'T WORK

    Those connectors are prone to failure.
  12. Andy-1960

    UK RCBO intermittent tripping advise??

    Why not swap the kitchen transformer with one of the other identical units and see if the fault moves.
  13. Andy-1960

    Japanese 3 Phase Wiring

    You will also need to check to ensure the equipment you have taken delivery of is suitable for use on our 50hz supply. Japan does not have a standardised frequency some areas are 50hz, others are 60hz.
  14. Andy-1960

    New to the forum

    Welcome to insanity.com!
  15. Andy-1960

    Hot SWA gland

    Why do people find it so hard to read a post properly and instead seem to take a guess at what has been written? The OP clearly states: There is 3 trefols running in parallel
  16. Andy-1960

    Hot SWA gland

    I would be interested to see a photo of this and the type of cable being used. What sort of current is being drawn to warrant 11Kv cables to be installed in parallel, I have never seen this done. Are you sure they are in parallel and not part of a ring or a tee’d radial feed? I have my doubts...
  17. Andy-1960

    3 phase to single phase with no VSD

    What size is the motor?
  18. Andy-1960

    SPD Question

    Yes.. both devices will require a protective device and should be connected as close as possible to the incoming supply.
  19. Andy-1960

    Shock from unplugged sewing machine lead

    Could it possibly be a counterfeit machine? The Chinese are knocking out some very good copies.
  20. Andy-1960

    Earth fault on a TN-S system

    How do you know it’s tripped on earth fault?