  1. D

    Advice on swa as tails

    you can get pin crimps for the 25mm that would allow you to install the cable to the earth bar. i would definitely earth the armour too but you shouldnt need to go as big as 16mm. 10 or 6mm should be fine. the only thing i would check for with regards to the showers is to try and calculate the...
  2. D

    Zs Problem

    lol @ Mark. aye you're probably right. well it is somehow managed to rectify itself and i am now getting a Ze reading well within what it needs to be. think it might have been an issue with the meter but whoknows. thanks for your help guys.
  3. D

    Zs Problem

    earth rods are intsalled around the gene. i am in afghanistan working and the ground isnt very good for getting a good Ze but i was still getting 0.15 ohms yesterday as a Ze reading so how this has changed overnight is beyond me
  4. D

    Zs Problem

    getting the same at the main panel. its powered by a generator and everything was fine yesterday so i am unsure as to how this has happened today. its an installation for camp accommodation.
  5. D

    Zs Problem

    in the db currently testing, the R1+R2 hasnt been higher than 0.20 ohms
  6. D

    Dimmer blowing

    depends what size of dimmer they have been fitting?
  7. D

    Zs Problem

    which ones?
  8. D

    Zs Problem

    Hey folk. i have been doing some testing and up to now i have had no problems. however today i have been getting a reading of >2000 ohms when doing a Zs test. i have been searching my brain and evrything else for a reason for this but cant find anything. this reading i am getting is right...
  9. D

    current carrying capacity of SWA cables

    i have the same problem right now in afghanistan.
  10. D

    all ideas welcome

    MCCB's wont fit in to the DB, already checked that option. thanks though. - - - Updated - - - thanks for that, i will have a search on the internet to source both options. thanks
  11. D

    all ideas welcome

    i am doing a job and the people that have ordered the materials have made a mess of it. i have got 4 x 3phase DB's, the isolators in these will take up to a 35mm cable, 50mm at a push. i have got 2 x 50mm feeds, a 70mm feed and a 95mm feed going to these. any ideas on the best possible way to...