Hi,
Going to be doing my Elecsa Assessment soon and house i have chosen to do the work on is a TNCS supply 6 way board with excellent access!! :)
currently it has 16mm tails from meter (located about 2M away on ouitside wall) earth is in 16mm and bonding is 10mm so not to bad!
however...
DurhamSparky
Thread
25mm
aus
electricians' talk
meter
meter tails
tails
Hi folks. Just like to pick your brains for a minute. The other day I had to fit a 63a 30ma (50a mcb) shower unit for a customer having a new shower fitted who didnt want a new consumer unit (old wylex board). Split the tails with a henley block but what a job connecting them in the unit. They...
DONKEY
Thread
25mm
aus
electricians' talk
shower
tails
through
unit
hello there
i've been squabbling with my pal about two supplies we have to put in for somebody.
edf are putting in new meters and we have to supply 2x 2 bed flats
i reckon you have to run 2x 25mm swa cables to each flat. (very difficult route)
my mate reckons you can run a 25mm t&e to each one...
Talking with a collegue today regarding meter tails.I went to look at a c/u change 80A main head on 16mm Tails i said should be 25mm but he said 16mm was ok 25mm for 100A main head. Whats the word out there with you good men ?
Cheers :)
Hi can someone tell me what the best way of running supply to cu from distributors supply if the run is more than 3 metres apart,as i have been told that you can only run 25mm tails no more than 3 metres,Thanks