Do you guys think that the majority of electricians actually bother using the adiabatic equation to decide whether the cpc of a T&E cable is adequate when supplying a CU in a garage/shed, or do most people just size the cable based on CCC and voltdrop?
I come across a lot of T&E strung between...
I am trying to get my head around the Adiabatic equation and was hoping that someone could check my understanding?
I know the equation is S = √I² x t/k
S = the CSA of the CPC
I = the PFC which is calculated from Uo/Zs
t = now this is where I get a little confused, my understanding is...
This one has always made me wonder !??
Does this work as simply for a 3 phase installation i.e 3.3kw over 230volts = 14.3 amps
so does 3.3kw over 400volts = 8.8amps per phase OR is it 3.3kw over 230volts divided by 3 = 4.8 amps per phase ???
Can someone please explain where to get the time (t) in the adiabatic equation
i can work out the rest just need the (t)
the MCB is a BS 60898 63A
my PFC is 940A
Thanks
Not got my reqs or on site guide with me today could some one explain or show me an example to work out earth size 230v supply ze = 0.12 customer been told about calculation rather than need to upgrade earth system and i cant remember formula or how to do it thanks in advance lads
I'm trying to get my head around using the adiabatic to calculate minimum size earth conductors and realised I am getting myself confused over which fuses they relate to and how they relate to the tables in the OSG.
This is a theoretical situation, I am just trying to make sure I understand...
so you use the adiabatic equation to work out the cross sectional area of a conductor
the fomula is obviously S=(sq root) of I2xt/K
can someone give me some numbers so I can work out the answer useing this equation as I want to make sure i know how to do it.
Can somebody have a look at this and tell me which tree I'm barking up?
Using the Adiabatic equation to determine the required size of main bonding and therefore the size of supplementary bonding.
Ze = 0.18
PFC = 1.3 kA
Fuse type 1361 IIa
S = square root (1300 x 1300 x 0.1) /115
= 3.57...
doing pir before cu change. property built 1968 imperial size cable all test results ok. just one circuit is bothering me and i maybe looking into this too much but radial circuit, which originally was for an electric old type two bar fire as informed by owner who lived there since it was built...
Hi all,
Completed my first pir yesterday (: now this client has got a three phase supply, TNS which feeds a ground floor shop and a flat above, the flat has a on peak and off peak supply. With the tails for the flat going into two kmf switches with a sub main cable of only csa of 10mm T+E for...
Hi all i was wondering if anybody could shed some light on this equation or part of it. I think i understand how to work out the equation its self but its this part i dont understand.
In order to apply the adiabatic equation we first need to calculate the value of I (fault current) using this...
can anyone help
I want to calculate a main earthing conductor for a three phase supply using the old adiabatic equation.
I'm struggling to work out what value of I to use. If you use 230V/0.35 (for a TN-C-S) then you get 657 amps.... if it turns out that Ze is lower, the fault current is going...
Hi people,
I'm not the best at math but I'm trying to figure out what size cpc for water bonding I can calculate.
Tns system
Ze 0.18
PFC 1.52kA
t=0.1 sec
K=143
8 metres in length
Main fuse= 80a, type 2, 1361.
It is currently a 6mm cpc but I can't replace it due to floors and new kitchen! I'll...
Hi
Is it acceptable to use the adiabatic equation to work out the size Main Earthing conductor to install in a standard domestic property for a consumer unit change.
Ive always been under the impression that its 25mm tails and 16mm main earth for a tns or tncs system, but a colleague...
Hi chaps,
Can someone please give me a quick lesson on adiabatics? When to use the equation, detailed description of what it is etc.
Been scouting any literature i have here but not been able to pin something down.
Thanks
B
yo, fittering about here tell me if im right.
example: identifying the minimum size of cpc required to ensure protectionfor copper conductors protected by say 50A tybe b mcb to .
so 250x250x0.4=25000 sqare root= 158.1/ 115=1.37..
so is this correct by multiplying type b by 5?
and my 50A...
Can any one help please
on a tncs system (PME)
100amp main fuse bs1361 100amp
I am trying to work out the maths for the earthing is there a simple way all looks a little confusing
S is the csa of the conductor 25mm
I is ???
t is page 244 the table says 630A
K = ??
so 630A squared x 5 (5sec...
Many thanks to 'Dave_' for posting this example originally in a thread.
Minimum Size of CPC
Here I will calculate the minimum size of CPC in accordance with regulation 541.1.3 of BS7671.
Primarily I will need to calculate the minimum size of CPC (or confirm the armouring is adequate) of...
does anyone know what the current limiting class 3 means on an mcb, for eg does this mean a max of 3ka let through energy ?
if it does it makes a difference when using the adiabatic equation for sizing cpc`s
Hi all have tested a flat were the main bond is only 6mm
the incomer is 1361 60A
main earthing conductor is 16.oomm
doing the adiabatic calculation what disconnection time would i use to assess if this conductor is man enough (and yes i know it should be 10.00 but the customer want have any...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc