I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs and the cable type is shown as 2.5mm2 type A install methord C. I suspect a clerical error but as it is in the vendor document pack what would you...
The accepted method of I.R. testing existing circuits has been to join L and N together and test to E, to protect against damaging any electronics that were inadvertently left in circuit.
However ,with the increase of new types of circuits between L and E as a result of "intentional leakage"...
Hi all,
First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the answer so I thought it best to ask!
I'm currently going through and renovating some of my property, and the garage wiring is of some slight concern to...
I have a question about mapping circuits in a single family home. I recently had my panel upgraded to an Eaton 2040 panel, and the electrical contractor who did the work did not label things very clearly, so my plan is to relabel all circuits from scratch.
As part of the upgrade he installed 4...
My 1990 property does not have the lighting circuits protected by the Distribution Board RCCB.Only the power circuits are protected.If I get a trip from the RCCB the lights stay on.
Do I need to upgrade my system to include RCCB for lighting?
Quick question, I done my compex a while ago but I seem to remember the instructor saying that if a circuit is intrinsically safe, then the equipment does not need to be rated for a hazardous area. Does this seem right? Site I’m working on has IS circuits going to valve control heads that...
Evening All,
Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board got fried supposedly after a power cut when the supply was restored. They were told they needed a switch fused spur fitted as there was no way of...
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on...
Hi,
Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario...
Hi,
I had a question in my head that turned out to two and then BANG im confused.
I need help with calculation here and explanation to get this right. If i want to build a lamp with 20 light bulbs in a 230V home. Each light bulb is 2watt.
How much current will they take when they are in...
Hello.
I'm in the UK, and have some questions/concerns about my kitchen set up. So the fuse box has 4 breakers/circuits for the kitchen (the lighting is on a different circuit).
One circuit covers the electric oven, gas hob ignition and a plinth heater.
I then have a single 20A rated...
hi guys
please help
1. i want to install zappi into existing CU with a type2 SPD
should i also protect 32A MCB for zappi with an SPD?
2. i have CU(hager VML410AH) with type A RCCB incomer only is it ok to fit SPD onto it?
thanks
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main breaker turned off. With all the circuit breakers turned off and powering up the main breaker to the panel I still have 123 volts across both (A) and (B)...
Hi everyone,
I have a particular job visited this morning, that on all circuits, at each point, i got a reading off around 25ohms for a earth fault loop impedance test(zs).
I then thought to do the same at the DB for those circuits. Again, same reading was obtained.
I then turned off the...
I had just installed a heat alarm on the downstairs lighting circuit during a kitchen rewire.
The new kitchen ring / cooker circuit I tested IR for L-N and N-E at 500v, fine, but the DS lighting circuit consisted solely of 21 LED downlights, in various rooms and the alarm. All of which say do...
Haven't been on here for a while, so sorry if this has been discussed before.
BS7671 2018 + A2 Regulation 421.1.7 recommends AFDDs for "single-phase AC circuits supplying socket outlets..." (requires in certain premises). My intention is that from September 27th I will recommend them to...
Can I run a 7.3Kw induction hob off of 2 x 16 amp circuits single phase I'm not sure what size cable is installed, I will check.
Would I be be able to run with the 2 x 16amp breakers or should I install a single 32 amp breaker with separate RCD?
Thanks in anticipation.
When I checked out this job I had a false sense of security from a recent competent looking EICR and two new CU's that looked to be fitted to a high standard. Most of the property does have a CPC on the lighting circuit, it's just this one room with a flat roof above that doesn't. This is where...
Guys needvadvice please
I was asked to carry out an annual inspction of a DB recently
There are 12 in number radial circuits suppling sockets wired in 4mm singles protected by 32A mcb the cables are enclosed in metal trunking and supply 13a socket outlets , are the mcbs now overated as the...