Hi, if I’m qualified JIB gold and wanted to sign off someone’s work and certify it for say a landlord can I? Even I’m not part of NAPIT or the like! Thanks Adam
4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall.
Current carrying capacity won't exceed 30amp.
Customer adamant they are fine because previous electricians have said they are fine.
What do you do? Tell him tough...
Surely if you fit an RCBO on each circuit, an RCD is not required?
Of course, a DP Main switch would be to cut all power, but like I ask, is the RCD required as it is incorporated in the RCBO?
Thanks
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables coming directly from the fuse box.
I've taken a photo of one of the light switches. (attached to post)
1. It has the earth attached to the metal switch...
So I'm getting various responses to this depending on how things are interpreted.
Here's a scenario:
Assume property is a tenanted property.
Assume cables are run buried in walls/under plaster (depth unknown).
Which of these circuits merit a C2 if they are not RCD protected.
1. Lights
2...
When there is a fault on an EPS circuit, how are we meeting the disconnecting times? Earth fault is easy - just use a 30mA B-type RCD, but for the overload, are MCB good enough? On a 3.6kW supply, the voltage will drop so quickly, will there be enough energy to trip conventional MCBs or do we...
Morning all, I am hoping to swap pendants and spotlights (which are on separate switches) that are above the kitchen island.
Is there a way of extending the connections and putting two pendants where the three spotlights are and the three spotlights where the two pendants are WITHOUT destroying...
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure.
Zsc= Zesc(or Zdbsc) + (R1+RN)
(R1+RN) = milli ohms/metre x length x correction factor and then divide that by 1000
Zesc = Uo divided by PFC
Then add together Zesc and (R1+RN)...
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and already done all the protective devices for all my final circuits but was curious if the distribution circuits need RCD protection aswell.
The project...
I am reviewing a EICR for a property I am buying. The vendor has had the EICR done, but both the Cooker and Shower are on 40A 60898 B curve mcbs and the cable type is shown as 2.5mm2 type A install methord C. I suspect a clerical error but as it is in the vendor document pack what would you...
The accepted method of I.R. testing existing circuits has been to join L and N together and test to E, to protect against damaging any electronics that were inadvertently left in circuit.
However ,with the increase of new types of circuits between L and E as a result of "intentional leakage"...
Hi all,
First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the answer so I thought it best to ask!
I'm currently going through and renovating some of my property, and the garage wiring is of some slight concern to...
My 1990 property does not have the lighting circuits protected by the Distribution Board RCCB.Only the power circuits are protected.If I get a trip from the RCCB the lights stay on.
Do I need to upgrade my system to include RCCB for lighting?
Quick question, I done my compex a while ago but I seem to remember the instructor saying that if a circuit is intrinsically safe, then the equipment does not need to be rated for a hazardous area. Does this seem right? Site I’m working on has IS circuits going to valve control heads that...
Evening All,
Strange one so after a bit of advice. Got called to a customer this evening who had their boiler repaired after the circuit board got fried supposedly after a power cut when the supply was restored. They were told they needed a switch fused spur fitted as there was no way of...
To my understanding it would be ideal to test and inspect before energisation, but it isn't 100% necessary. If it leaves a client without power, it breaches health and safety (no power to safety services etc) or inconveniences them I'd have thought it would be reasonably practicable to turn on...
Evening all,
If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or fitting RCBOs, is it permitted to add additional sockets to the circuit via RCD spurs or additional RCD socket outlets? (type A of course)...if the sockets...
Hi,
Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario...
Hi,
I had a question in my head that turned out to two and then BANG im confused.
I need help with calculation here and explanation to get this right. If i want to build a lamp with 20 light bulbs in a 230V home. Each light bulb is 2watt.
How much current will they take when they are in...
Hello.
I'm in the UK, and have some questions/concerns about my kitchen set up. So the fuse box has 4 breakers/circuits for the kitchen (the lighting is on a different circuit).
One circuit covers the electric oven, gas hob ignition and a plinth heater.
I then have a single 20A rated...