conductor | Page 3

conductor

  1. S

    Main Protective Bonding Conductor question

    Hi guys Would appreciate your comments on the following.. I am currently involved in the refurbishment of a building with 2 service heads (both in use) but only one gas intake and one water intake. What are the main bonding requirements in this situation? I am assuming both MET's require a...
  2. V

    SWA cable , TT, do i need an earth conductor in the cable?

    At the origin the installation is TT. Plan is to install a submain to a new db. Not carried out all the calcs yet, but my question is does the swa require an earth conductor in the cable. Basically planning on running a phase and neutral or perhaps even 2 x phases and neutral.(the cable will be...
  3. B

    Defining what equipment has protective conductor current

    Hi all, I have an engineer who has failed a wall mounted data cabinet because the PDU is hard wired into a switched fused spur, the spur is spurred off a ring main in 2.5/1.5 twin and earth. He has failed it under regulation: 543.7.203 The wiring of every final circuit and distribution...
  4. T

    Main earthing Conductor also bonds water

    Domestic TNCS, main earthing conductor runs to water pipe, bonds via clamp with label, cable is continuous, then runs on to MET in DB. Seems wrong, but cant find specific reg to say so....any thoughts? Thanks, Timotei
  5. P

    High Zs on SWA Armour / New Earthing Conductor

    Hi all I am after some help/Advice if possible please A SWA sub main Distribution circuit has been given a Code 2 Rating on a recent EICR due to a high Zs of 2.8 ohms. The cable is 180 metres long and runs underground in ducting. The Install is from a few years ago when a new Substation was put...
  6. D

    confirmation of earthing conductor size

    Hi Guys just a quick question but what the hell do I put in confirmation of earthing conductor size when the earth is the swa
  7. leep82

    C.P.C in T&E as a live conductor

    I know the thread title sounds bad but hear me out. I have wired an intermediate switch set up with feed at one switch, switch wire at another and twin and earth as my strappers between to an intermediate switch. My customer wishes to use lightwave switches for the three posistions mentioned...
  8. C

    protective bonding conductor size

    Hi guys, I've questioned something at my workplace and after receiving my answer I'm not overly convinced and would like some other experienced gods to chime in :) On a new install in an existing property today I went to bond the Water and noticed it was already done, clearly many moons ago...
  9. B

    Main Earthing Conductor and Earthing System question.

    Hello all, Just a quick question regarding I+T that I wanted to get some clarification on: 1. I recently went to a job where the incoming cables from the street came up through a metal conduit from the ground and then ran through some metal trunking before terminating in three sealed fuses...
  10. GBDamo

    High integrity earthing.

    i understand the need, as I see it any circuit with a likelihood of more than 10 mA earth leakage should be subject to high integrity earthing. This requirement can be achieved by many methods and I can see the sense in some. Using RFCs instead of radials gives two paths so in the event of a...
  11. R

    Coordination between conductor and oveload devices

    A good memory trick for exam conditions for coordination Ib In Iz (Alphabet) the earlier letters are always lower in value than the earlier ones, saves remembering Ib < In In < Iz Ib < Iz
  12. kingeri

    Extraneous conductive part as bonding conductor

    Been nosying about at my brother's new house this week and fixing a few bits and bobs. The electrical installation mainly dates back to the early 80's at a guess and apart from a few broken accessories and a lack of RCD protection (now fixed) it has all checked out okay. PME earthing. Today...
  13. Andy78

    EICR - Undersized earthing conductor

    Doing inspections today and found a couple of properties with under sized earthing and bonding conductors. Earthing system is TNC-S and features 6mm earthing conductor and 6mm bonding conductors. I normally code 6mm bonding conductors as C3 and am happy to do so here too, but should I be coding...
  14. Jim90

    Circuit conductor query

    Hi Guys, I have an electrical installation certificate following a periodic and under the ‘circuit conductors csa’ CPC column, someone has put ‘MW’ Unsure what this person means by this. I was thinking like a conduit earthing system etc. Other columns show MICC and SWA under CPC so I can rule...
  15. J

    Supply conductor size for 8 bedroom Victorian house

    Hi folks, I've recently visited a large 8 bedroom Victorian house. It has a three phase supply. One of the phases feeds the main house, its wired through a 100 amp main switch/ isolator. The Suppliers Side is 25mm tails but the customers side to the main house consumer unit appears to be 16mm...
  16. J

    What code? bonding conductor

    A connector block has been used to extend a 10mm water bond, what code would you recommend? Thanks
  17. Michaelwgroves

    Can you join Main Protective bonding conductor

    I have a 6mm main protective bonding conductor from a 1981 install; adiabatic equation says this is sufficient and no signs of thermal damage. (Discussed in separate thread). Gas was not bonded, it's a big job to run new cable so I've used redundant water bonding as now all plastic to bond gas...
  18. Lee Gold

    Calculate the resistance of a copper (annealed)

    what's the difference annealed? Calculate the resistance of a copper (annealed) conductor 35m long that has a C.S.A of 2.5mm2?
  19. Marcus Vaughan

    6.0mm earthing conductor to MET on TNS

    Hello. I am carrying out an inspection on a domestic TN-S system. First observation is that I can see 16.0mm earthing conductor fro CU to MET - but then is steps down to 6.0mm connecting to the supply cable. This should be 16.0mm - shouldn't it? I am going by table 54.7 in the big yellow book...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top