Hello,
Board change today (domestic), cable is aluminium twin and earth - socket ring = 4mm/1.5mm, lighting = 1mm/1mm, oven 10mm/4mm
IR all good, continuity & Zs are within values set for copper equivalents.
This is not tinned copper.
I have managed to find out that this cable was used...
Evening everyone..
I have just undertaken an EICR and there is 6mm bonding to both water and gas at the correct points (within 600mm of entering building), however they must be joined somewhere as there is only one 6mm in the CU. I believe this would be ok if the conductor was unbroken but...
An outbuilding is fed from a separate single way board in the house and has a 2c 4mm SWA to the building of 7m. Its a TNS. This outbuilding has its own water main (albeit in plastic) which comes directly from the water meter not through the house. Testing between copper pipes below the sink and...
pete89987
Thread
bonding
building
conductor
copper
outbuilding
plastic
submain
Hi all , my local church warden has asked about the testing
of the lightning conductor as part of a general checkover of
the electrical system , told him I would find out on here !
Is this a "special test" that has to be carried out by installers
of the conductors or can I do basics such as...
Was doing an EICR yesterday at a block of flats, was taking my ZE @DB and could not get a reading, so went to the external meter box to find that 6" of the earthing conductor from the neutral cut out had been cut out (Stolen?) I looked in the other 4 flats meter boxes and all but 1 had the same...
The EC appears to be clamped to the water pipe just before going outside to the spike. Was this ever standard? Its a TT with Ze of 36 ohms. Is it best practice to run a separate EC and water bod to MET. (no gas in house).
Hi, I own a top floor apartment in Swansea. The lightning conductor above the roof of the apartment block runs through a channel along the edge of the roof which is permanently flooded with rain water (except after long dry periods) to a depth of 25-75mm. This doesn't seem safe to me. I would be...
Gary Were
Thread
channel
conductor
installation
lightning
protection
water
We are testing a very large production plant with multiple Air Handling Systems with multiple ductings fed from each system, all systems are fed from the same sub-station package, would we have to connect to each ducting service to satisfy a "tick in the box" under services bonded, we have...
Being inquisitive this afternoon I decided to put my clamp meter on the main earthing conductor of a large commercial electrical installation I'm on at the moment. The supply is 2500A, with leakage measured on main incoming Earthing conductor to METwas nearly 5 amps. Any thoughts?
Always bothered me when bonding the Earthing system in a building to the lightning conductor installation, it seemed odd to me. I went to Elex today and attended an NICEIC seminar about earthing, apparently Tony Cable is saying it's OK as long as you install a surge protector unit between the...
Hi all
I am looking for ideas for best practice for Earthing Conductors to a dual tariff CU. Should two 16mm Earthing Conductors from the MET be installed, one to each earthing busbar? Or one earthing conductor to one of the earthing busbars and a link of 16mm to the 2nd earthing busbar...
Been asked to install an extractor in bathroom. Installing 30mA rcd spur outside covering all lighting and ext fan. Obviously notify building control and installation cert. what's people's opinions of listing as a departure from bs7671 on installation cert. obviously recommend upgrade to 16mm...
I need to work out if I will be required to run a separate protective conductor along side the swa cable I'm going to install. The cable is a sub mains feeding a 3 phase db panel in a large workshop. The cable is going to be a 50mm 4core 120 metres steel wire armoured installed in a underground...
Cant quite get my head around how you use this reg?
Lets say S =16
I = 657
k = 115
You have to work out t first of all so
t = K2S2/I2
so t = 7.843409 (to 6dp)
therfore K2S2 = 3385600
The reg says that we need to make sure that K2S2 is greater than the value of the let through energy...
Hi
In commercial location I need to run 8 individual RCD protected circuits to 8 D/Skt outlets, each run is in 2.5 singles in plastic conduit about 20m max in length.
My question is can I run a single cable earth ring to each skt and if so what size should it be, Worst case is all 8 skts...
Was asked a question today and want to confirm my findings after reading the regs
we have a 1000A main supply (1000A ACB ) and from this we have 2 sets of supply conductors, 1 goes to a 600A Panel Board the other to a 400A Panel board with the tails being contained in a metal trunking, we plan...
hi,
Just reading through 'Connections' (ELECSA's magazine).
Found an article saying it was aright to use the green/yellow for a SL in a class II fan if you sleeved it both ends with a brown sleeve.
They cited 514.4.3 which in my book refers to PEN conductors saying it overrides 514.4.2 (thou...
I was reading the latest issue of the NICEIC’s Connection magazine, when came across an article about wiring extractor fans. I didn’t read it in depth (was in the library at the time!!!), but from what I can gather you can now use the cpc in a flex (flex only, not hard wired) as a live conductor...
I have a TNC-S System (PME) , with a 100A fuse, the main Earthing conductor is 10mm, terminated in an earth block, with main bonding conductors of 10mm.
Tails to consumer unit are 25mm with 16mm earth. The Ze of main Earthing conductor is good.
British gas put an isolator last year and at the...
Fella's
I'm just writing up an EICR from last month, one of the findings was a lighting circuit on the non RCD side of the board where the cpc was used as a strapper in 2 way light switching, Ive marked it as C2 for two reasons, one being that there is no longer a cpc in the cable and also that...
LlandrilloSpark
Thread
cable
coding
conductor
cpc
eicr
however
insulation
live
practice
schedule