Hi All
Please correct me if I'm wrong I was thought that an RCD should trip when you come In contact with a live conductor. Now I have had 2 electric shocks in the last 3 months and on both occasions and the RCD did not trip.The RCD was tested and passed.
Any ideas ?
Lilyrose08
Thread
conductor
contact
live
might
people
rcd
spark
tripping
working
wrong
Seen something today while performing a fire alarm test at a relatively sized office that struck me as strange. Thought there was no better place to query it than here. Like I said decent sized office, 3 phase tn-c-s supply can't really say too much more about the installation because this...
Hi, testing a UNI with one main supply, which in turn feeds around 10 separate building. Each building as it own Gas supply with meter, so therefore a Protective Bonding Conductor to each incoming supply. Does the size of the cable have to correspond to the incoming supply size, or to the size...
Hello, I am studying to pass the 17th Edition and there is a question that i do not know.
The following final circuit are to be installed using thermoplastic insulated multicore non-armoured cables 3x6A lighting 1x20A UPS supply 3x32A ring 1x40A cooker. If the cables are enclosed in a...
Im doing some alterations in part of a school. I noticed a water stop cock that has no bonding conductor. Its not the main stop cock as that is another part of the school. I carried out an R2 from the local sub board i am working from and got 0.32.
Am required to bond it to bring it within the...
Can any of you designers out there tell me how you go about sizing the conductor from the Star point of the transformer to earth?
By this i mean if there was a HV earth electrode around a 1000kVA transformer made up of 2 X 70mm bare copper conductors onto a common earth bare this would give a...
Can anyone tell me if a test is to carried out to establish the resistance of earth electrode for a generator providing alternative supply
1)what must be agreed before test can begin?
2)Action to be taken with earthing conductor for generator before testing can began.
Action to be taken with...
gurungtp
Thread
before
conductor
earthing
generator
question
stand
system
tt system
B. Gas decided to a. relocate a customers meter and b. connect it to the gas main in plastic. The old meter was removed leaving a stub of pipe with the MPBC still connected. My view is that this is now an earth rod, auxiliary to the distributor earthing conductor.. Another guy looked at it and...
Ok, so I am in college studying a level 2 course (2365) and its coming to the end of year were we have to do a practical installation and then testing. I've taken the test once and failed.
My tutor, taught me and others things that are contradicted both in the On Site Guide, a book by Trevor...
Hi guys I done a quick search but could not find a answer, earthing system in question is TN-S. Supply cable comes in is terminated into two 1361 cut outs and then one set tails then go through to next door into another 1361. Am I wrong in believing that in order to test ze properly the next...
Hi,
Just want clarity on earthing conductor sizing. I know the table but wanted to know what people recommend about a earthing conductor within a PVC/PVC cable, is this earth big enough for the new board or run a separate earth at least half the Line conductor ( rule of thumb )
Thanks
I have a 3 core t+e on a 2 way switch and when it is turned off there is still 45 volts at the light. I have stripped this down to a 1 way switch and the voltage disappears. I then meggered the 3 core and it is clear. There is continuity through the conductors and no obvious fault with the...
I understand that the 16mm coming out of the service cutout is my main earthing BUT the 6mm from the m.e.t which goes to the sub db has thrown me out. Do I put down 6mm as this is lower case
Iv just complete an eicr. I have a few queries.
1. Page 2.part k.I'm unable to get hold of the details for the Characterisitics of primary supply over current protection devices- can I put lim in these boxes.
2.page 2. Part L. Main protective bonding. There's no bonding as the mains water...
Hi Guys
I have been asked to quote to install a MET for a TN-C-S system and I could do with some advice please
I can't get into determine the size of the conductors as I cant switch the power off to open up the main panel
What I did was measure the circumference of the SWA it was 214mmm I...
Hello everyone. Been asked to upgrade a consumer unit from the old rewireable type. The current set up has like 1mm in earthing conductor, does anyone know was this EVER legal???? Have a look at the pic, you can hardly see it it comes from the MET behind a wooden board into the CU.
Hi folks,
I'm project managing a 30kW PV installation on a social club and could use a bit of advice -
Main board is an old Ottermill F frame (the board has no plates; I had to track down an ex Ottermill employee who ID'd it from photo's).
We'll be installing a new TP&N 3 phase sub-board...
Hi,
Had to change a bathroom fan at the weekend for someone and they wanted it to be on a timer, but couldnt as the cable was buried in the wall and wouldn't move etc..
the cable that fed it was a three core flex, I the earth was not being used anyway due to the load on the end etc.
I know...
Hi I am working in a hotel and I found that a 3-phase DB was fed by 2 seperate swa cables one containing the 3 phases and the other a seperate neutral and earth I know this is bad practice but can someone tell me why the NIC firm have picked this ad a fault I would not have done this myself it...