I've got a question regarding whether its acceptable or not to connect two different sized conductors (or even two equal sized) into the terminals of a main isolator.
this is the set up
TNC-S 3 phase supply incomer 100A main fuses > 25mm tails into 100A (switchfuse) Main isolator >...
I've gone around in circles several times on this and I'm still not completely sure what the answer is ... generally speaking, when changing a domestic CU in a house that has a TN-S supply and 6mm2 main bonding (which is in good condition) is it necessary to upgrade the main bonding to 10mm2?
I...
Hi All,
I have been searching the forum but can't find this anywhere. Can you please see if my interpretation of this is correct:
50x50 trunking, 2m run with 1 90o bend.
4 x 50mm conductors,
1 x 35mm conductor.
As there are no factors for over 25mm2 I have to work it out manually
50x50 =...
Hi
doing R1 + R2 on lighting circuit green probe on cpc
Red probe on Switch line (switch ON) or Line.Which is correct? Switch line to confirm polarity? .took readings on both .why is switch line reading higher. Thank you for any replies.
Angus
Why is it when you cross connect the conductors at each leg and then test continuity, the result is one quarter of the combined resistances of the legs? I am usually pretty good at seeing how/why calculations work out, but just cannot in this case get my head around why the value measured is a...
hello peeps,
I could do with some help. And i will greatly be appricated to egt the help.
What is the min CSA of live conductors suitable for CCC and voltage drop for the following:
a. 3kw, 230v water heater
b. 11kw, 400v MIG welder
c. 12kw, 400v three phase machine
d. 5kw, 400v three phase...
Hi Guys and Dolls
In my 2004 edition of the IEE Inspection and Testing Guidance Note 3, page 78, Protective conductor continuity can be confirmed with an Earth fault loop impedence test (R1 + R2 or R2 is not required to be measured). (Note 4)
Ring circuit continuity also does not have to be...
Hello, This is the first time iv came across anything like this and i went to quote this fuseboard for a upgrade yesterday and had a look inside and did all the required testing and inspecting and said id get back to them with a date when i can do the installation but came across one slight...
elecypwn
Thread
and earth
aus
conductors
cpc
earth
electricians' talk
old
twin
twin and earth
I had a search with no joy.
I am trying to find a reg to state if its ok or not to use 1 continues 10mm conductor for gas and water Main Protective Bonding . Having a look at a new CU install where there is no MPB and lighting CPC at all . Fun Fun Fun
:clap:Thanks
cablemonkey
Thread
aus
bonding
conductors
electricians' talk
main
protective
Both Basic & Fault Protection
SELV – if anything is provided by SELV, this gets a tick, otherwise N/A. Examples would be 12v extractor fan or 12v downlights
PELV – if anything is fed from a PELV supply
Double Insulation – Anything double insulated, i.e light fittings etc. These may also have...
sxsparky
Thread
cables
conductors
electricians' talk
guide
protection
sheet
test
this is what i have down at the moment.......is there anything that you guys would add?
An earth fault is the most common fault in electrical circuits. An earth fault may consist of a circuit breaker tripping, a fuse blowing, or an RCD (neutral to earth) instantly or it may not re-engage.
The...
p11jor
Thread
aus
conductors
earth
electricians' talk
fault
fault finding
finding
help
project
switch
Had another dispute with who i was working with today, with testing an new installation. Here goes
I always thought that the proper testing sequence is R1+R2, continuity of bonding, insulation resistance. Then ze, then zs. rcd
But the person i was working with today told me i should always...
Replaced an old fuorescent strip light with new fitting as old one was tripping lighting circuit. Problem still there, wiring looks fine. Tee puzzling thing is it trips when you switch the strip light off. Swiching it on is fine!
Any ideas?
zyderboy
Thread
aus
between
circuit
conductors
electricians' talk
fitting
help
lighting
lighting circuit
needed
problem
screw
tripping
Going slightly off piste on my D&V Project again.
I'm thinking of running parallel conductors for an electric gate supply 'just to learn about it'.
After reading the BGB it seems quite simple, in that the sum of two smaller cables will be the Iz of the circuit as long as the cables are roughly...
I've just been to a flat tonight to look at some potential work, but there is no bonding conductor to the incoming water pipe inside the flat.
I had a quick look in the main distribution board cupboard of the flats, but could see no evidence of bonding to the water, and the main water incomer to...
alanl
Thread
aus
bonding
conductors
electricians' talk
flat
protective
hello can anyone help me all i want to know is are 4mm main earth and main bonding conductors ok? as in passing a periodic inspection?
its a tns
external is 0.06 ohms
pfc is 2.9ka
talis are 25 mm
and it has an 30ma rcd main switch
i always asumed to minimum was 6mm but someone is questioning...
Hi guys, i have a question what size of bonding conductor is required for A shed that has a 63 amp 3 phase( 25mm2 swa) supply going to it. It is supplied from the main building that has a 400 amp TN-S 400mm supply . hust want to see if you have the same answer