meter tails | Page 3

meter tails

  1. R

    Meter tails over 3 metres???

    Good morning Looking for some advice on a domestic job. The consumer unit is being moved from kitchen to cupboard in hallway. The meter is staying in same place but the distance between meter and board is around 7 metres. I have been advised to fit a 100amp isolator at meter and run tails from...
  2. M

    Meter tails and capping

    Hi guys came across meter tails buried less than 50mm no rcd protection but did have some red capping over and they are in prescribed zone about a meter between main fuse and consumer unit. TNS system. C2 or no code??
  3. A

    Meter tails issue

    Hi guys I'm installing a CU in a new build and have a couple of questions I need some guidance with regards to the meter tails. I need to drill a hole through the wall (for the meter tails) to access the main supplies which are located in the recessed box on the outside of the property. I am...
  4. N

    Ok to use concentric cable as meter tails??

    Been asked to do an eicr on a flat above a shop. Tails are run in concentric cable from isolator switch by the meter, to the main switch in fuseboard. Never run into this before so not if this is still deemed acceptable or not? Any advice, reg numbers? Thanks in advance.
  5. L

    Cut meter tails

    Working on a new build site i've come back to a property that i'd 1st fixed to find someone has cut all the cables going to the exterior of the house including the 25mm meter tails in the meter box. The house has been boarded so renewing the cables isn't really an option. What would be the...
  6. ThatMatt72

    Meter Tails in Galvanised Trunking...Is that a thing?

    Hey all, Excuse the ignorance here but I wonder if you lovely folk might have any opinions or better still be able to point in the right direction in the BBB. I am being asked to move a CU from its current position, behind a fitted kitchen, under the sink and totally inaccessible, except to the...
  7. D

    16mm meter tails, long run

    Hello all, I am working on a property & they need the consumer unit changed. The slight problem i have is the tails are on 16mm. But the meter is approx 10-12m (tail length) from consumer unit location. Is this length permissible. There is a KMF at the meter but the customer does not want the...
  8. juice

    Meter tails protection

    I work with temporary electrical installations to construction sites at the moment and have a query related to supply arrangements. The supply earthing sysytem is a TT type. The main cut out fuses I've been told are 200A and the supply tails are 70mm in a three phase arrangement. These 70mm...
  9. J

    commercial meter tails

    bit of reassurance on coding I have 3 phase 3x150a (checked with supplier) incomer feeding meter in 50mm tails- 5omm tails to 3x blocks from meter from each block tails to various isolators all not exceeding 1m in the same cupboard, the highest fused isolator at 60a being fed with 16mm and...
  10. P

    E7 boards and meter tails

    ok a couple of questions ill keep it simple its been ages since I had anything to do with E7, is an E7 board supplying storage heaters still ok on a non rcd board ie classed as fixed equip ? who is responsible for the tails? from head to meter and meter to board thanks
  11. mattg4321

    Meter tails in cavity

    Ok own up who's done this? I try my hardest to never do this but have, on very rare occasion installed meter tails in a cavity as the lesser of evils. Would be interesting to hear real world thoughts on this and potential work arounds so you don't have to. I know someone on here posted a while...
  12. haptism

    Meter tails over 3 meters

    Hello, anyone know when the regs recommending a switch fuse for meter tails greater than 3m long was introduced ? On older installations (about 20 years ago) was a switch fuse required on tails over 3m ? Thanks
  13. Msitekkie

    SWA For meter tails?

    I need to upgrade my meter tails to 25mm. The existing tails pass along under the pebble dash in plastic conduit (which would be too small), then apparently at an angle through the porch structure (unprotected) then turn sideways into a void & up the void to CU. I have seen other posts where...
  14. 8

    Max length of meter tails

    Ive been asked to look at the electrical installation at a large 5 bed property with an attached annexe that the owners are converting into a 2 bed holiday let. There's one supply cable that comes into the annexe for the entire property . This is currently routed via a single meter to a CU . 2...
  15. R

    Meter tails & Protection

    Had a look at a job last night and the customer had another electrician bury the cables with a bodge method of protection (they were planning on plastering over them as they are) (image attached). The tails run from the meter (out of view at bottom floor level), up into the ceiling and to the...
  16. leep82

    Routing of meter tails

    hi all any advice on the following scenario much appreciated. I have taken on a rewire from another electrician whos personal circumstances mean he cant finish the project. Majority of the first fix has been completed including the repositioning of the DB. The original DB was situated inside the...
  17. G

    Pyro meter tails, can they stay or need replacing?

    hi all , im having a new consumer unit fitted ,but my meter tails are in pyro its a 1970's 2 bed terraced house.. im just waiting for my electrician to confirm if he can re use the pyro tails or they have to be replaced with something more modern. can anyone confirm yes or no have they got to...
  18. I

    New here... and here is a an interesting DB I've come across... need some help with EICR for it!

    Hello, I've got a question that I thought I throw out to the crowd and see what comes back... I am a little stuck with a recent EICR that followed a change of occupier. The home is 30 ish years old and has been extended several times. It is a fairly large home with swimming pool, multiple...
  19. R

    Fuseboards for sale and Meter tails ....cheap

    hi I have 2 fuseboards for sale with 2 meters of 25mm brown and blue Meter tails ,along with 2 x 32mm compression glands and 10 blank plates. Wylex 15way fully loaded and wylex 10way fully loaded ,brand new in the box metal clad 17th edition compliant Looking for £160 for everything...
  20. B

    Recommended Wholesaler for 95mm singles / meter tails & accessories

    Hi We have a new 3 phase 200A supply installed which is to supply 4 flats & a low load landlord supply. We need to source 95mm singles that will connect from the ukpn 3 phase head into a stand alone isolator which will then connect into a 3 phase distribution board that will supply the 4 flat...