As part of a large waterfall installation I'm installing a single phase 0.75kW motor with time clock and need advice on the overload setting please! I was told anything above 0.5hp/0.37kW required a contactor with thermal overload?!
I'm aware the 3 phase calculation would be...
kW/ Vl x sqrt 3...
Hello folks, not posted in a while, been busy. However this week I have been slightly busier than usual.
I completed my AM2, results due tomorrow morning 8 AM...
I did the PRE AM2, I did find it a big help. Glad I did it.
AM2 consisted of the following - Risk Assessment, Safe Isolation. There...
At work there has been a problem I've been told about, small 1.8 Kw 3 phase fans tripping the overloads
I'm not really involved in this but I am interested......
The fans are run off Inverters and the OL's for any circuit are usually within the control panels, length of run is upto 35 metres...
Evening All,
Is there anyone that knows what tests are required when carrying out injection tests on a Crompton Thermal motor overload type CR 12 /13 model.
Thanks
Sparky 63
Hi
I'm due to get my kitchen replaced and will be installing x2 2400w plinth heaters so will I require a seperate circuit or can I connect them to my ring circuit ?
Hi
has anyone recently done the am2? I just wanted a basic calculation for setting the overload (they give you motor rating in Kw) for the 3 phase dol motor. I have tried looking this up for last few nights, but keep getting inconsistent or over complicated findings.
and people at work say...
Holiday let sleeping 8+. Gas ch (combi) and cooking. 2 x Wylex rewireable cu's, pme (6mm earthing conductor!), no rcd protection. 16mm dno supply, prob 100A dno fuse, no rating on meter but likely to be 80A
1 x cu for normal (lights, rfc's) etc. 2nd cu 60A rating with 3 x 45A fuses feeding 3 x...
I have an issue with a three phase submersible pump. The pump is controlled via a 55v control panel. The panel consists of the mains isolator, the 240 - 55v transformer for the control circuit, relay, contactor and overload. The pump works off three floats, one start one stop and one high level...
a big hotel group has asked us that they want 2 way dbs in each bedroom feeding one socket and 5 lights all led fittings, but they want the supplies to boards daisy chained from 10mm t&e or swa feeding 4 rooms per circuit. the only way ive ever done this is sub per board, but cant find anything...
Hi,
I'm an apprentice electrican. Please could someone give me some guidance on this as I am confused? Thanks.
What is the difference between overload rating ie 6amp on a circuit breaker and breaking capacity on a circuit breaker ie 10ka?
I'm confused.
Thanks
:)
Hi.
I am new to D.O.L but have sussed them out except I have one scenario I still need help with.
There is a single phase pool pump which is set to come on with a honeywell single channel 7 day time clock.
I have wired the D.O.L as single phase with a 230V coil.
The problem is I need the...
Hello. I need advice about choosing MCB for cable overload protection.
I'm using BS7671:2008 Requirements for Electrical Installations.
Reg 433.1.1 has 3 requirements:
1. Ib <= In
2. In <= Iz
3. 1.45Iz >= I2
I don't understand reason of 1.45Iz >= I2.
And I think this requirements are...
Hi,
Just came across something earlier that made the have a think.
Distribution panel fed by 25mm cable.
This goes directly in to a D50 breaker.
The D50 feeds 4 6mm cables squeezed in top of the MCB that feeds small 3 phase bus bars, these in turn feed 1.5mm circuits.
I have fitted MCBs to...
Hi all,
Could some one explain the correct way in connecting a 3phase contactor with overload protection.
I have the supply going into l1, l2, l3 and motor connected to the load terminals, t1, t2, t3. I also have the 230v connected to the a1 coil and neutral on a2. Just a bit confused...
hi guys if installing a shower consumer unit with a 63amp rcd main switch and a 100 amp OPD PRIMARY SUPPLY then main switch is of a lesser value than the main over current protective device how do we get around this.
Right following on from my last post.
i rewired a pizza oven circuit as the oven was being moved.its done in 16mm twin and earth.protected by a 50 a mcb.
guynfoned tonight saying after half an hour the circuit tripped so went up the oven is 13 kw can this be an overload?should I put a 63a mcb...
Hi guys in installing a 16mm submain with a 10mm earth and I'm going to install a 80amp time delay RCD with a 63amp MCB to protect it. Some one said I could just use a 63amp RCD to protect it? Never done this before and wouldn't think you could.
Also should I just use a 63amp RCD with a 63amp MCB
Hello,
I am an IT Tech and not an Electrician so please excuse my ignorance... I have three monitors, one 860W computer and multiple other devices including printers etc.. plugged into 2 x 7 UK Power Socket Extension Cords which can be found by googling the following: Belkin Conserve Smart AV...
Hi Guys I hve a ring main that keeps tripping, but it also trips the main rcd on the board, is there a possibility that it is being overloaded? There are about 6 computers a franking machine a photocopier coffee machine and a few other gadgets on this one ring of 10 sockets! Should the ring be...