Scenario encountered:
New submain looks to have been taken from a PME supply in 4c 10mm SWA with no copper earth to a external metal feeder pillar.
The SWA has been glanded into new metal clad DB within the feeder pillar effectively incorporating it into the PME supply. A Earth has also been...
Had a interesting phonecall a moment ago with western power.
Have a customer wanting a ev charging point, so checking the supply and due to the old cut out appearing as a TNS and also having a PME sticker on it, I rang western power; they said that its now PME as according to the records there...
hi all i was just in the middle of doing an eicr on a caravan park and wanted some opinions on what codes are relevant to the site.
ive got tncs pme 100a 3 phase. each phase feeds a db like in the picture by a 100a main switch and 63 amp mcb and 10mm pyro (earthed with bonding clamp) which in...
Evening gents, just seeking a little advice. Recently bought a new place, it has mostly been rewired, its on a TN-CS system. The garage which is approx a 40m run from the house is supplied by a 2.5mm cable believe it or not, it is donkeys years old. This supplies a 2 way rcd board in the garage...
Hi
I have lurked here a while but have never posted before.
I have been to a site this week with a view to put some motors on some gates, however the current installation needs some attention.
The site is a builders yard sited probably 20 meters from a large house the yard is supplied by 10MM...
Hi all , im new here but have always looked for answers over the months
description of my question
there is an external 100 amp 3 phase metered head that this new 10 bed house is to be fed from , the builders installed a 35mm 4core swa as i directed however they forgot about a 16mm earth
now...
Hi,
Just a quick query for others views please.
Customer had a brand new three phase supply put in in April. I have been called in to rectify the ---- poor work carried out so far. The first thing I noticed was there is no main earth. The 3P head has a green PME sticker, but there is no...
It's proposed in the 18th edition that any new pme installation is to have a rod added by the electrician that has has a resistance of 30ohms or less. What are people's thoughts on this? My main concern is the amount of services that are going to get hit with everyone driving rods in.....also my...
Afternoon all.
Just had a weird one and was wondering if there was some regulation that I'm not aware of or if I've missed something stupid....
The DNO have brought in a new PME supply to a purpose built (permanent) shed in a field where there is going to be a new build domestic property later...
I have been called to a job that has an fault unrelated to this question.
When conducting checks to earthing and Main Bonding I noticed the earthing arrangement has been converted to PME, there was also no main Bonding.
I have attached a picture, I am a little sceptical to who has altered...
Hi all, I've been surveying 12 blocks of flats today with a view to doing full eicr's on the lateral mains and landlord lighting supplies. All the main services terminate at a Henly distribution board with no cut-out or main fuses. See pic, I've done very little on pme supplies and wonder if...
Been on a job today and debating what to put on the certificate.
The DNO in early 2013 upgraded the supply and installed PME. The previous setup had an earth rod installed. This is still connected to the main earth terminal. Not sure what type the previous set up was as the customer is none the...
hi I'm a part qualified electrician gaining exp wherever I can whilst doing my college course.
Today we were hooking up a static caravan with 3 core swa. All was good until we started doing the tests. With the pme connected I was getting 0.26 as an earth loop at the board in the van. The boss...
I'm installing a 32A socket on a PME system.
The socket itself is indoors and is on its own RCBO.
The intention is to use the socket for power for outdoor events.
My technical help line says that I should disconnect the earth at the socket then TT it. It seems to me that that would make it...
Metal farm building currently has single phase TT supply with all the required bonding in place.
Client requires a 3 phase supply for a piece of equipment in this building - is it possible to bring a 3 phase supply from the farms house which is PME?
I have a situation whereby a new build property has had a green electrical cabinet installed at its boundary, and a new 3ph PME supply installed.
There is a 4c 25mm SWA from here to the detached garage, which will house the plant room (3ph ground source heat pump, 3ph PV inverter), and then...
I am going to a job this afternoon, new shower circuit. I noticed yesterday that the Wylex CU has a 100mA S-type RCD as the main switch and all the circuits are on 30mA RCBOs. PME system as far as I could tell (certainly not TT). Didn't give it much thought then, but was thinking about it...
My question is not quite in the title.
I've been asked to quote for the above. No extraneous conductive parts in garage, which I intend to supply from spare way in house domestic CU, swa to garage CU utilizing the earthing facility of TN-C-S.
However, one of the reasons they want the supply...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc