9 LED outside garden lights protected by RCD. Originally the client asked me to investigate outside lights as when he switched them on RCD tripped immediately . On investigation found previous Halogen fitting past sell by date most full of water and corroded. Client agreed to have all replaced...
Hey just a quick one,
The factory I work at have built a new maintenance shed, and each work station has a 3 phase outlet rcd protected. Now, my problem is every time I make up a board which contains contactors it trips the rcd.. Is this due to some sort of balance issue? Can some one clear...
Hi All
I have a prob i hope someone has come across
clients RCD is tripping at odd times. Doest seem to be any pattern or any specific piece of equipment causing it. Not one particular circuit either...trips on downstairs ring, upstairs ring, lightings ...you name it.
Wont reset until all mcbs...
Circuit: -
17th edition board with 30mA RCD
Pond pump circuit is a 16A MCB feeding double pole FCU with 3A fuse, this feed an electronic immersion heater timer, this is connected to a pond pump/filter unit via SWA.
Problem: -
RCD trips every time the pump switches OFF
What is connected to RCD...
Hi Guys,
An elderly customer has just moved into her new flat, unfortunately her heating on E7 doesn't work. The E7 dist board RCD is tripping (probably as it kicks in).
She has two boards, one normal and one E7. The E7 board is feeding three night storage heaters and an immersion heater. All...
Hi All,
I have a 2400w power saw on 230v which is tripping after about 0.3 seconds. It is running of a 16A RCD with no other devices on the circuit. Could this be caused by a high current demand at the start up or is it more likely to be something else?
My calculations reckon that it should...
Andrewbullie
Thread
anything
breaker
power
rcdrcdtripping
start
tripping
hi
i have an old customer who's pv installation is tripping out when raining/wet. 16 x 245w Sharp panels with a Power-One PVI-3.6 TL inverter. The inverter is showing a current leakage from the panels which obviously increases when soaking. All mounting structure is bonded
There is a 30mA RCD...
I recently got called to a rcd kitchen circuit tripping, so I removed all appliances as normal but still tripped so carried out IR test which showed no fault? any ideas no fault found?
craigday
Thread
carried
circuit
fault
rcdrcdtripping
still
tripped
tripping
Hi guys. slighty baffled by this one.
Rcd tripping intermittently when 3x 16watt 2d lights are switched off at the wall switch. Carried out ins res tests... All ok. Lights turn on fine and only trips 2 out of 10 times when turning switch off. possibly inductance causing earth leakage??
Hi all
After having the shower circuit upgraded to 10mm cable, new shower and pull switch the tripping times recorded for the existing rcd are as follows.
76ms x1 65ms x1(180) 28.6ms x5 38.3ms x5 (180). These times appear not to meet the standards for the minor works cert and im after...
ambrad
Thread
after
electricians' talk
getting
rcdrcdtripping
results
times
trippingtripping times
within
Hi guys, what would cause an RCD to trip when carrying out a Zs test, it is a lighting circuit in a new build house and I have it on the "no trip" setting and it still trips the RCD, the RCD itself passed the RCD tests and the IR is 800Mohms so that's fine, I even even replaced the RCD but the...
nicsin02
Thread
electricians' talk
lighting
rcdrcdtripping
robin
tester
testing
tripping
using
while
Will a RCD trip if there is a problem on the cable drawing no current ?
I plug in a tumbler drier and power it up, the RCD trips
Remove the drier plug and try the drier in another socket. The drier works without tripping the RCD.
I try my electric drill in the socket that tripped the RCD...
Have been to check site where consumer unit with 5 circuits. 4 of those circuits feed various light and sockets in one stable barn with a lot of flourecent strip lights and outdoor school flood lights. The 5th circuit is on 16A mcb and feeds a second consumer unit via armoured cable in a second...
Can anyone offer some advice......
Customer recently moved into property, underfloor heating not working but looks like quite a new install. First problem i found was the switched FCU was faulty that supplies the underfloor heating - replaced that, switched on still nothing illuminating on the...
Hi Every one, I have been asked to look at a problem in a toilet when the light is turned off the RCD trips intermitenetly but not when it is turned on. There is a fan and small flourescent shaver light in the room . the instalation was rewired by me about 10 months ago all the test results were...
Hi all, new to the forum and hoping to garner some of your expert knowledge.
I live in a small 2 bed house and the main RCD on the consumer unit keeps tripping randomly.
There are 6 separate circuits and by elimination I've ruled out the lot except for the sockets (all on one ring).
Now I'm...
daerve
Thread
electricians' talk
fault
fault finding
finding
help
help please
please
random
rcdrcdtrippingtripping
I have a split CU and have just added a new ring (14 sockets) a 10.5k shower and lighting circuit. All of these are as a result of a third floor being added to the house. Everything works perfectly but when the shower is on and I use my drill in any of the 3rd floor sockets, the RCD trips. I...
Adders1
Thread
electricians' talk
fault
floor
load
rcdrcdtripping
shower
sockets
tripping
under