I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but using the same socket it kept tripping the rcd. Socket next to it worked okay.
Replace double socket with a new one. At the same time ran an earth wire...
hi all
come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and the electrak tap off leads terminated into RCD under desk sockets
why install RCD sockets when circuit is protected by 32A RCBO
is this install correct...
Hi all,
Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A.
I have been tasked to install temporary power in the form of a single 16A commando socket outlet for the purpose of feeding a boiler to maintain heating in a building owned by the...
Hi, just hoping for a bit of advice. When I travel abroad (Europe, predominantly Spain/Cyprus) I usually take a single travel adaptor and a UK 4 gang extension.
As they're getting on a bit, I've just ordered replacements and am thinking of putting an inline, non latching RCD between the plug...
Hi
I am asking for help as a novice and 1st time user of this forum.
Recently started to experience tripping of MCB & sometimes with the RCD at random times, intervals can be days after resets or several hours.
Could an appliance or appliances be overloading the circuit?
How can I test an...
Hi everyone,
I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection.
The client has specifically asked for them to be plug and play and rcd protected, which is fine as they are under 32amps.
I will be running in 5 core swa's for...
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an existing lighting circuit via an unswitched fused spur, if the lighting circuit has no RCD protection am I allowed to install it?
Same question for if...
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by their buttons before starting work.
But on completion of work, one of the RCCDs, when tested via tester, would not trip, the other operated as expected!
Hi all,
Curious one and hopefully some one of you could give me some advice.
A customer has had a steeltech shed installed at their premises. A large one. Wants 3x light fittings and 5 double sockets intalled. There's an electric roller shutter door on the shed also to be plugged in. My plan...
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be used to aid with selectivity and avoid potential nuisance tripping, providing the ratio of the rated residual operating current of the upstream S-Type...
Hello All,
I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual current-operated circuit breaker on the supply side (25A, 30mA trip current). The RCD is there because some of the circuits supply power to outbuildings...
Called out to fault on RCD tripping maybe twice in a month for sometime.
Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which made matters worst.
So refitted original RCD Type AC for the time being.
Insulation Resistance measurements were 20 M ohms.
Ring continuity fine...
Hello
Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January.
Existing is a TT system with a solar installation fitted.
Current install has a 100A TP incomer, meter, C63 TP MCB, solar install, 100ma RCD, distribution board fitted with...
Hi,
I have a job for a customer, the consumer unit is an old 3036 board and there are several holes in it giving access to live parts, I can change the consumer unit but when put on an RCD the sockets trip. IR readings on the sockets are low but the customer isn’t in a position to have them...
Hello!
I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me to do a battery storage setup, specifically with EPS for battery power.
I'm stuck on my RCD selection because basically, I'm going to shift 4x...
At my place of work we have just had multiple LED advertisement screens fitted outdoors, the company specified 16amp RCBO’s for each set of screens. On powering up, the circuits were nuisance tripping due to earth leakage. So the company who installed swapped the rcbo for MCB’s.
The screens...
My builder has sprung a job on me.
New circuit required for a hob.
The CU has a single 30mA RCD, type AC.
I am still unsure exactly when I should insist on type A, and when I should just advise.
Would you guys be insisting on type A in this case, thus fitting a new CU (as it is an old NSB wylex...
Good evening,
I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently trips when I switch on the Central Heating on and sometimes after running the heating for a couple of hours. The heating is gravity fed, hot water...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc