  1. rustynails

    Insulation resistance on a lighting circuit

    Today I got 0.11 Mohm L-N>E at 250v then the same at 500v on a 6amp lighting circuit wired in the 70s which is the only lighting circuit for the house. Customer did not want me to remove the lamps. I forgot to ask or see a bell transformer or aerial booster. No faults known to the customer. MCB...
  2. S

    High zs reading on a radial circuit

    I have a high zs reading of 312 ohms on a radial circuit, r1+r2 is 1.82. Earths seems fine in the sockets....any suggestions?
  3. S

    Testing lighting

    Hi guys ive not done any real testing on commercial jobs other than fault finding etc and was wondering, when dead testing lighting circuits would r1+r2 be accurate as the r2 will most probably not run the exact same route as the r1 with more connections etc so would you do an r2 flying lead...
  4. uksparks

    What the heck are you reading?

    Just laying here looking in a book.... The mrs says, erection? What sort of book are you reading? Eh? What you on about? It says erection on the front... Its Guidance Note 1... What did you think it was?
  5. D

    Very low reading of PFC test

    hi, I did Ze test, I got 0.22 ohms but PFC test I got 22 Amps. it is very low. I am expecting a (230/0.22=1045 amp ) by theory So pls let me why it is very low reading
  6. Paul.M

    Leeds Vs Castleford Wembley

    Picked up my tickets yesterday, shirt ironed, car fueled up and WE ARE OFF TO WEMBLEY :willy_nilly: Should be a great game and maybe a modern day classic. Both teams will give it 100% just to have the bragging rights within our local area, Cas fans will be drowning their sorrows tonight though...
  7. D

    Meter Reading check / inspection - PV System

    Thought I had posted this back in Jan, but looks like it didnt post. A meter reader turned up unannounced to take a reading/inspection of the PV installation at my setting, said this was normal and would happen every 2yrs !
  8. S

    megger mft1730 earth loop reading

    hi I was on a job testing incoming supply on a TT systems the earth loop reading was 2,53ohms now what my question is It was a 2 commer 53 i am guesting that means 2.53ohms if you test result are lower you get 0.12 (point )why does it change to a commer or am i reading it wrong
  9. S

    2394 practical

    Hi everyone, I have my 2394 practical coming up soon and wanted to know if you can do a global insulation resistance test rather than individual circuits and if the assessor would be happy with this, just thinking it would save a lot of time when carrying out all your tests.
  10. E

    Maximum ze reading help.

    Hi. I have have tested a property with a TN-s system and the main ze reading is 2.98 ohms which is far to high for a TN-s system which needs to be within 0.8. What would be should be done in this situation? Contact electric board? Thanks.
  11. S

    R1+R2 of a ring circuit

    I know you take the highest reading, though not sure if you take the highest reading on the ring circuit or a spur off the ring circuit? cheers
  12. G

    Eicr earth rod over 200ohm

    Earth rod measures 247 ohm, with water and gas connected 233ohm. All covered by 30maain rcd. C3? Improve the rod reading to below 200?
  13. S

    MICC Cable - phase to earth fault

    Hello Gents, I have a low IR reading on a lighting circuit - the circuit is 50 years old - i believe the fault is at the pot connection as there has been a downpour of water on this connection - I was going strip back the sheath and identify the point where the IR reading...
  14. P

    Low ir reading

    Isn't it ok to join the live and neutral together and test down to earth? I did this today on 250 volts as there are dimmers on the circuit and lv lights and a smoke detector. Having done this I got readings of somewhere around 1.6 m ohms. I left that circuit as it is not urgent to finish it yet...
  15. J

    Insulation test between 2 different circuits

    Hi scratching my head alittle today as of why when I test between two different circuit I was getting 55 meg ohms on L and N and 1700ohm on E. It is a horse stables and I can see one cable goto the the right hand side stables and the other stays in the left side stables, I thought it might...
  16. N

    IR reading

    Hi guys job today for nuisance rcd tripping ,I thought it was an appliance as I explained in a post yesterday but turns out it wasn't . Anyway disconnected the only neon I could see , unplugged everything run an IR test ,great neutral to earth but earth to live 0.02 . Checked every socket , I...
  17. M

    problem with halogene light ,voltage reading 288 V !!!!!

    hi everyone , this is my first time on this forum , anyway this is my story why I am here writting to you , 6 month ago my mother and father in-law wanted to change the lighting in the new house they bought and they find a set of light from homebase they really like , because they was eco...
  18. C

    Lighting Circuit Problem

    Hi All, Just returned from trying to locate an issue with an upstairs lighting circuit - with the circuit L/N/E disconnected from the board and breaker I get he following readings:- (a) Type 2 Insulation Resistance Test = 49.7 taken at 250V (b) Voltage reading on the (dead) circuit of 3.5V...
  19. L

    fluke 1652c continuity readings

    Does anyone else have problems with there continuity readings my readings never seem to be stable for example a newly installed ring end to end resistance on neutral and line ill get .46 and then a reading of .04 on line end to end the leads are always nulled and I even check readings on calcard...