Hi
What is the installation reference method for flat T&E cable, with capping and buried in plaster, am I correct in thinking it is method C as all the others in table F6 (page 150) in the OSG refer to insulation?
Steve
Hi, designing my first small installation which i will be using for my first assessment with Elecsa/NECEIC etc ( any thoughts on which way to go appreciated). Installation is in an oak wooden framed and mostly glass conservatory with instruction of no visible wiring please! The obvious way...
Just trying to get something straight in my mind. I've been looking at the Electrical Safety Council's Guidance 6 for changing a consumer unit in a domestic premises. They say that if the customer does not wish for a full EICR then the pre-work survey required before the CU change should...
Where more than one type of method is used do you record each one used? i.e A/B/C
Or do you record the most common one?
Also cables buried within a block wall, i.e chased in & capped or equivalent which do you use?
Has anybody got a chart for quick reference that can show me volt drop, i know the calculation but just wanted a quick reference table. Can any body help?
Hi
I am having trouble determining between reference methods. Which reference method is it for flat twin & earth cables in joists under floor boards and in the ceiling in a domestic property?
which reference method for-
example- upstairs sockets that are 95% run between joists for the first floor. ?
where there are more than one reference method ie. one section run in an insulated wall and alsoanother section in plaster on a masonary wall.
kindest regards
Hi chaps
Just a quickie....what is the general reference method for domestic wiring these days....say down stairs ring main..ran under floor boards and chased in2 wall?. and also upstairs lighting where it has been chased in2 wall and laid on the insulation in the loft?. Cheers Steve.
Completing my EIC's for assessment tomorrow with the NICEIC ... I'm used to using Elecsa certs and haven't come across 'Reference Method' before.
Changed CU, tested all circuits. Most of the cables are run either through the plasterboard walls (not in conduit, no thermal insulation), or...
Hi
I wanted to see if anyone has any question or answers on the new EICR forms.
I will start with, Does anyone know what "location reference" means in the schedule of inspections?
I am trying to get hold of a copy of the Electrical Safety Council technical manual. its proving really illusive! does anyone know where i could get hold of a copy.
cheers
One of the Technical Reference Documents that NICEIC stipulates for assessment is BS7671:2008 – Requirements for Electrical Installations including Latest Amendments (IEE Wiring Regulations).
What do they mean by Latest Amendments (IEE Wiring Regulations) and where can I get it from?
Thanks.