Hi everyone.
I basically wanted to check to see if what I propose is correct.
I had an electrician come round (pre covid) to install power to my garage (Detached from house). This is the setup he used.
Spur off socket on ring main a short distance to a 13A switched FCU
Cable from the FCU...
I know the title is super vague but I have details here is the problem/context..
I recently had my kitchen done (including the lighting) which has caused two of my sockets upstairs to stop working.
The house's had a previous extension so some of a ring circuit up stairs is also down
I have an extension lead thats runs
2 60watt uv bulbs constant
2x 10watt constant heatmats
Its a 4 port masterplug with surge protection and shuttering wasnt cheap.
Now i have need for 1 more plug for a waterfall i didnt account for another 10 watt plug but no socket.
Can i use a...
Hello guys still waiting on confirmation of a rewire I've posted a few questions for, this is another question I’ve got in mind, fairly simple.
The front reception will have a tv going on the wall on the chimney stack.
Just wanted to know how many sockets do you guys put in for this? I was...
Hi,
I have a Martindale EZ165 and have used it previously to do basic earth loop test on sockets in the UK.
I want to carry out the same operation in italy- it's a rural house on a TT system, I want to know if the approximate Zs reading is below 200 ohms and that the sockets are all correctly...
Klik plugs are rated at 6 amp with 075mm flex.
But I have seen them used on 10 amp breakers in shops and the like with the plug in Rose's and with the Marshallling boxs?
How does that work if the plug is only 6 amp
Is it due to the flex length being so short or something else?
Just your thoughts on this one,had the plasterers moaning about live sockets.
Added a couple of sockets to an existing ring main,to keep the power on in the house I’ve connected & taped the cables & neatly coiled into the flush box.
The customer knows the reasoning behind this,& will talk to...
Evening all
Got a query excuse me if not seeing the simple logic. On reading regs book it states can install one unfused spur off ring in 2.5 but if more sockets required need to first wire through a fused spur. My question is, is this all because of possibility of overloading one leg of the...
Hello,
The shed is supplied with 6mm Swa on a 25amp rcbo. Inside the shed is a 20amp socket circuit and a 5 amp lighting circuit.
Can I add a junction box to the supply cable about mid way and radial off that box to a double socket?
a 32amp radial requires 4mm, and a 20amp radial is 2.5mm...
Can someone tell me when it became a requirement for sockets (domestic property, use by ordinary persons) to have RCD protection. Or rather, a flat completed (first sold) in Sep 2007, with no RCD protection for anything - would that have complied at the time.
I don't have any earlier regs. that...
Hi all,I found a 6mm “cooker” circuit feeding 4 sockets in the kitchen as a radial. R1+R2 tests fine and Zs is low. Can’t see where they are jointed but it goes from 6mm to 2.5mm. If everything tests fine, can’t see a problem leaving it as is. Will have to downsize the mcb as it’s currently on a...
Hi
We have had our single garage damp proofed (tanking system) it took a a good few months to work due to the amount of damp present(garage used to flood over time - back wall attaches to neighbours elevated garden 2/3 of the wall is agains ground).
we’ve had the tanking done and it has...
Afternoon all,
Just bought a house with a remote garage, said garage has no power or lighting.
I'm hoping to use the garage as a gym and some storage so I'm looking to install 2x 5ft LED batten lights (45w) along with a wall switch and 2x double wall sockets.
Found this off-grid solar kit and...
Been asked to supply 13a sockets to 2 positions round a sports facility. The expected load is small, but the length of cable run is fairly long. I’ll probably be using 10mm2 2core with the swa as cpc.
They have had problems with kids etc gaining access after hours and fiddling with things etc...
A friend of mine has installed a BS-1363 socket in their bathroom, well outside of the zones (but not 3m outside) and protected by a type A RCBO which is itself downstream of a type AC RCD. The friend installed the socket in a 40mm back box, and when (s)he moves house and gets an EICR, the...
Some background info.. maybe you can help. I have a den that was running 600-800 watts worth of electricity and on the other side of the den is the living room in which I had another 1100 watts running. One day I plugged in a standard lamp cfl light bulb and noticed it dimming as if the current...
Hi. Please let me know if you need more Information. In my kitchen one socket fused and will no longer work. The only thing plugged into it was a tasting coffee maker.
The double wall socket had a kettle on the other plug. And that works fine. The switch on the tasting plug no longer switches...