Hi all, its been a while.
Is there a reason why I cannot have two separate shaver sockets in a bathroom.
Failed EICR section 6.3, "More than one item of equipment providing electrical separation in one room (2 shaver sockets)"
Thanks
Hi
I have a site where they have some sockets fed via Three Phase and Neutral and others TP with no N. Rather than both types of sockets for both types of appliances, was looking at 'standardising' and upgrading all plugs to TP and N. And where the appliance did not need a N, it would be left...
My electric sockets keep tripping, this happens every hour or so after flicking the trip switch. This happens even when nothing is plugged in at all and the sockets are even switched off, I've done nothing to disturb the wires and taken all the sockets off to check for damp and loose connections...
Can I ask if anyone can give any advice please.
I am in Scotland.
Well in a nutshell:
Electric Kept tripping - did not know why
Electrican came out to check, said Neutral/Earth was wrong way around on one socket, and switched them back he said.
Soon after half the sockets in flat stopped...
Charge two devices simultaneously without fear of fluctuations within the power supply interfering! The load isn't split across both ports on our USB sockets, so you are guaranteed optimum charge every time!
To find out more on this product visit: https://www.scolmore.com/products/usb/
Hi, Newbie here so please excuse any stupid questions. There is a single 2.5 T&E running from a dedicated connection on my "old type" fuse box (photo available if needed) in the garage to a single 2 gang 3 pin socket (approx 3 metres away) - there is no return cable. I'm wanting to add extra...
Hi everyone.
I basically wanted to check to see if what I propose is correct.
I had an electrician come round (pre covid) to install power to my garage (Detached from house). This is the setup he used.
Spur off socket on ring main a short distance to a 13A switched FCU
Cable from the FCU...
I know the title is super vague but I have details here is the problem/context..
I recently had my kitchen done (including the lighting) which has caused two of my sockets upstairs to stop working.
The house's had a previous extension so some of a ring circuit up stairs is also down
I have an extension lead thats runs
2 60watt uv bulbs constant
2x 10watt constant heatmats
Its a 4 port masterplug with surge protection and shuttering wasnt cheap.
Now i have need for 1 more plug for a waterfall i didnt account for another 10 watt plug but no socket.
Can i use a...
Hello guys still waiting on confirmation of a rewire I've posted a few questions for, this is another question I’ve got in mind, fairly simple.
The front reception will have a tv going on the wall on the chimney stack.
Just wanted to know how many sockets do you guys put in for this? I was...
Hi,
I have a Martindale EZ165 and have used it previously to do basic earth loop test on sockets in the UK.
I want to carry out the same operation in italy- it's a rural house on a TT system, I want to know if the approximate Zs reading is below 200 ohms and that the sockets are all correctly...
Klik plugs are rated at 6 amp with 075mm flex.
But I have seen them used on 10 amp breakers in shops and the like with the plug in Rose's and with the Marshallling boxs?
How does that work if the plug is only 6 amp
Is it due to the flex length being so short or something else?
Just your thoughts on this one,had the plasterers moaning about live sockets.
Added a couple of sockets to an existing ring main,to keep the power on in the house I’ve connected & taped the cables & neatly coiled into the flush box.
The customer knows the reasoning behind this,& will talk to...
i have completed a wall and patio for my sister
i was going to progress with the electrical work myself
but been told NOT TO
so taken heed to wise words
i have now contracted 9 local electricians
for a price not one reply as yet
so my are plans are installing 8 outside lights and 5 outside...
Evening all
Got a query excuse me if not seeing the simple logic. On reading regs book it states can install one unfused spur off ring in 2.5 but if more sockets required need to first wire through a fused spur. My question is, is this all because of possibility of overloading one leg of the...
Hello,
The shed is supplied with 6mm Swa on a 25amp rcbo. Inside the shed is a 20amp socket circuit and a 5 amp lighting circuit.
Can I add a junction box to the supply cable about mid way and radial off that box to a double socket?
a 32amp radial requires 4mm, and a 20amp radial is 2.5mm...
Can someone tell me when it became a requirement for sockets (domestic property, use by ordinary persons) to have RCD protection. Or rather, a flat completed (first sold) in Sep 2007, with no RCD protection for anything - would that have complied at the time.
I don't have any earlier regs. that...
Hi all,I found a 6mm “cooker” circuit feeding 4 sockets in the kitchen as a radial. R1+R2 tests fine and Zs is low. Can’t see where they are jointed but it goes from 6mm to 2.5mm. If everything tests fine, can’t see a problem leaving it as is. Will have to downsize the mcb as it’s currently on a...