Loooking for a bit of ideas on a issue if have with a RCD. 4 circuits on a submain that i recently changed, above the board was a leak so intally thought the problem was related to that. When carrying out the RCD auto test when it came to x1 the meter read error and would not trip. If i set it...
Had a look at a fault for a mate, cooker kept taking out main 30mA rcd when switched on at cooker switch (no load, just turning on at wall)
Disconnected cooker, turned on all ok. Cooker faulty? Had it tested and it was fine.
Tested circuit, megger, r1+r2, all perfect. Went to do zs and...
Did an RCD test on a new consumer unit, but got a fail on 1 times, but passed on 1/2times & 5 times.
Thought it may just be the rcd so i checked my instrument on the second rcd, but was perfect.
So then i swapped the rcd over & tested again but same happend again failed on 1 times but passed on...
Is there a time limit this has to be done in? Basically I did a bit of work for someone who was building a new house but not all of it, it was finished by a relation of his, unfortunately I didn't know at the time he's a bad payer! He's now been living in this house for 6 months and whenever I...
A client is asking about fwt and they want 20% done each year, the building is now 5 years old, where in the regs does it state that 20% testing is allowed, as the grey area is the last 20% would then be 9 years out of date and not 5.
Hi there,
I was testing the supply of a fridge with a voltage indicator.
I tested the incoming suppy which was fine but when I tested the terminals on the compressor it tripped out the mcb.
Why would this happen if Im using a voltage indicator and not shorting anything out as such?
Thanks
Hi there was wondering if a PAT with barcode scanner is any use on items that already have barcodes.
Does it depend on what tester was used in previous tests carried out by another company??
Hi all,
Today i came across a bit of a problem and to be honest not sure where i stand.
Was called to go and look at a small job, to add a couple of extra sockets to a kitchen. Nice and easy surface mount. When i looked at the c.u it had been installed april this year, so i thought great rcd...
I have been given very old panels from where I work. there are 20Cells on each panel and I have tested both at 2A at 9-10V. Open CCT voltage is not much more than that.
They are 4"x4" poly silicon cells.
I am in Ireland so no real payback of a proper grid tie system.
I have a large 1500VA UPS...
Hi
OK, got an extention lead thats shot (not mine) With only a Fluke 1651 NOT a pat tester I have 96 volts between CPC and phase yet an IR test shows >500 M ohms. ? How would you test?
Kind Regards
David
I have just tested a ring and the IR reading between N & E was 0.00 M Ω, N & L was 0.13 M Ω and L & E was 0.14 M Ω. I have removed all the loads and tested with a Fluke at 250 Volts. Plz could someone point me in the right direction to locate the fault.
Further more the Ze was 0.08 and...
Have a senario where a 30mA trip cuts out whenever a Commercial dishwasher starts the electric pump in its initiation cycle.This equipment is on a radial circuit insulation tested and sound, the Dishwasher has been checked by the installers with no faults. If this cicuit was isolated and set up...
Hi all
Anyone got any thoughts on this....
TNS arrangement
ZE = 0.65 ohms
ZS on tested circuit 0.85ohms
RCD >1999 on 0.5 x
28 & 32 ish ms on 1 x
> 40 ms on 0 & 180 degs although the unit did pass on 0 degrees once or twice before failing the 180
Tested my Megger against a known...
Hi guys,
I was testing a new house yesterday that we have wired at work, i came to test the lighting circuit in the lounge and sun room, the lounge tested out ok but then in the sun room i tested to line and earth without the switch in the on position and got a reading.
So i then did a bit of...
Hi, just tested a fuse board:
1*main switch
lighting circuit
lighting circuit
smoke alarm circuit
-----------------
1*rcd
Oven
Sockets
Sockets
Sockets
Security Alarm
Water Heater
-----------------
RCD failed 1x with ?400ms reading (megger MFT)
performed the ramp test and the RCD tripped at...
Hello All
We've been asked to test quite a large Corn Starage/Drying plant. The installation was put in in 1979 and has never been tested since. We have all the blueprint drawings, but cables are not marked at each end (i.e control panel and isolator).
When I've been round other sites...
Is a socket hanging out a wall, barriers and enclosures, functional testing of accesories,
or something else I thinks is the first one but a mates says no if its out the wall it cant be operated normally, just Sunday pub debate
Pict
Hi all its late and i`m tired:confused:,
Just fitted a new shower in my own house, question is, i have installed a new circuit for shower.
can i get away with a minor works?
been so long since i`ve just installed one circuit anywhere i cant remember if it`a minor works, or full EIC cert.
and...
I have been testing an installation with lot of RCBOs recently and found that a significant proportion of them will pass at 30mA fail at 5X30mA.
SO FAR:
Tests have been repeated several times over a year and the same ones fail at 150ms but pass at 30ms,
Most other RCBS pass without problem...
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc