I have been asked to provide a supply to 2 x containers on a contruction site (1 for materials 1 for tea hut) with sockets for battery chargers etc. The supply at the house to be refurbed/extended is TN-C-S.
Reg 704.411.3.1 prohibits use of TN-C-S unless to a fixed building.
Could...
knight1
Thread
aus
electricians' talk
site plan
supply
supply to
tn-c-s
I'm interested in collating the differences in the requirements (not the definitions) between TN-S and TN-C-S.
I've aleady seen an example in another post tonight: "TN-S Ze max is 0.8", Any other quotes (with regs reference if possible)?
Why would someone want to go and put one in on a PME system?
On a closer examination, I noticed that the main earthing conductor had been removed from the PME cut-out!
So, had the spark who installed this electrode just gone straight in, done a Zs which appeared excessively high without...
Staffie
Thread
and earth
earth
electricians' talk
electrode
tn-c-s
hi all.
i may be completely wrong but on a tn-c-s system if i was testing at say a lighting point, lighting circuit breaker off but main switch on then i would have continuity between neutral and cpc, right? but then by my reckoning if i were to then open the main switch then the continuity...