  1. V

    Callout Today on a TT Install tripping RCD

    I got called out this evening to a tripping RCD on a TT install after a lightening strike in the area. Its quite an old CU with mcb's and a standalone 100ma RCD on the tails between the supply and the 100A DP main switch on the board. The RCD would switch on but as soon as the CU main switch is...
  2. F

    Isolator Tripping RCD when switched off???

    Hi, I left work today after carrying out a test everything tested ok so energised the installation and no problems (new install). However when i switched OFF the isolator to the board before the main switch on the board, one of the RCD's tripped (split board). It was the end of the day so have...
  3. sajeel

    Electric Oven tripping rcd

    Hi people, Need your advice recently wired an electric oven onto new twin rcd board. Oven was working on previous rcd and was recently purchased about a week a go. Was working fine on old type cartridge fuse board [emoji33] . When I did insulation reading it would fail when I turn isolator...
  4. C

    brand new Bosch oven tripping rcd when cycling just the fan.

    just replaced a 15 year old whirlpool fan oven with a new bosch £700 touch. last night I was checking to see how much each oven was using power wise, by monitoring it via an elios4you solar pv/house monitor. I turned off the fan oven after about 1 minute, by first turning the stat to 0 then...
  5. D

    's plan underfloor heating relay tripping rcd

    Hello All I'm currently wiring up an underfloor heating manifold to an s plan system. the heating boiler takes its power off a ring main in a new loft. All circuits in the split consumer unit are RCD protected. I'm following the wiring diagram given in honey well wiring booklet ed 16. Page 14...
  6. S

    Glass washer tripping RCD

    Hi there. I was wondering if someone could help me... Glass washers are not my usual 'thing'.. The Lambrr glass washer in my girlfriends work is tripping the RCD. It was tripping every time she tried to turn it on and start a wash cycle, so I opened it up, fixed a small leak, dried it out...
  7. S

    X-ray Machine Tripping RCD

    Hi there, First post so please be patient. I was called to our local vets as there X-ray machine would trip the RCD at the consumer Unit when they went to switch it on but when they re-set it it works fine as it only does this the once. I can not find any faults with the fixed installation and...
  8. HappyHippyDad

    Intemittent tripping RCD.

    Hello everyone.. I have a job tomorrow tracking down a tripping RCD fault. This would have panicked me a year ago, now I'm looking forward to it and cant wait to get there! However, from the phone conversation I have discovered the following: 1. No recent DIY work or professional work has...
  9. M

    Zs test tripping RCD.

    Hi, recently I have found that my Fluke 1653 has been tripping the odd RCD when doing a three lead Zs(loop) test. I can't understand why, it has not done this before.
  10. P

    LED lighting tripping RCD

    Hi Guy's, im looking for a little professional guidance, I have recently replaced my kitchen lighting from compact fluorescent and GLS lamps with LED down lights and strips. Both switched from a double wall switch, single pole. The entire down stairs lighting circuit is protected by a MEM M6...
  11. B

    N-e fault on non RCD side of db tripping RCD???

    As above... Possible?
  12. L

    Zanussi ZKC6040 new bottom element in top oven tripping RCD

    Hi Peeps, Had a job where the base element in the top oven had gone on a Zanussi ZKC6040. No problem fitted a new element, swiched on, put hand on the oven base sure enough started getting warm, bosh, job done, thank you very much and see you again! The next day customer phones to say the RCD...
  13. C

    Newly installed Consumer Unit is tripping RCD's when hoover or kettle on

    Hi all, I'm new here so bear with novice questions pls. I have renewed an old CU (the one with pull out fuses) to a very new one with 2 rcd's and 10 MCB's. the old one had the kitchen sockets and the 1st floor sockets on the same ring (weirdly). Layout is this: RCD1 63A with: 1 x 40A MCB for...
  14. C

    new hob circuit tripping rcd - giving me headache

    Hi all, have taken over a 2nd fix right at the end, just turned power on, hob circuit is tripping rcd in split load board, the polarity is correct, have done continuity on l-n-e getting 99.9kohms and 299mohms insulation resistance on the hob supply cable, however when I test between n and the...
  15. B

    Bosch appliances tripping RCD

    I have a customer who has recently bought a new Bosch fridge freezer. On plugging it in the RCD trips as it goes through it's start up cycle. I have tested the RCD and all is fine. Bosch replaced the appliance and same thing happens with the new one. A Bosch engineer has now visited and told the...
  16. G

    Potterton Suprima boiler tripping RCD

    RCD for the boiler trips when the hot water light is illuminated. Have done an RCD test to rule that out which was ok - where would be the best place to start to diagnose? Cheers.
  17. HappyHippyDad

    Tripping RCD since testing?

    I have literally just had a phone call from the customer I saw today after doing an EICR and he says one of the RCD's is now tripping every half hour or so. There were 3 CU's in total so I am back tomorrow to finish off. I didn't have time to test each circuit on the third CU but I did find...
  18. M

    Harmonics and tripping RCD

    I have just completed an installation on a fruit farm which all tested 100%. There are 3 x 3 phase pumps 32a 41a & 41a, only 2 run together at an one time. When the second pump is started the 100A 100mA trips out. The pumps are run from variable speed controllers on a three wire system, no...
  19. B

    Problem with shower tripping rcd

    Hi Peeps. I'm having an issue wiring in a new shower in my house that I'm having trouble working out. I initially wired in a 8.5kw Tritn shwer thats a few years old but had never been used and kept in the box. I ran the circuit in 10mm T & E (circuit length 15 metres). I installed a 45A pull...
  20. M

    Immersion Tripping RCD

    Hey folks just looking for some info here.. Im after changing my element for my immersion as it kept triping the RCD.. I installed a backer bt7 7" Rod, I wired it the following, (1)Live to The Element (2)from the other side if the element I connected it to the L on the immersion (3)Neutral to...
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Back
Top